I think you’ll find it stated in the Blue Planet installation manual. I’ve 
installed dozens of their systems over three years and never paid attention to 
cable length. One solar self consumption system I let run over the winter 
without ever reaching a full charge and the cabinets didn’t drift more than 10% 
SOC from each other. Blue planet does recommend a full charge at least once per 
month for balancing though. Matched cable length, again assuming properly 
sized, really doesn’t matter anymore.
________________________________
From: RE-wrenches <[email protected]> on behalf of jay 
<[email protected]>
Sent: Tuesday, July 20, 2021 4:13:41 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Lithium battery cable lengths

HI Barton,

OK so please explain how the BMU/BMS is controlling watt hrs between the 
batteries as I’ve not heard that this is possible.

The batteries are Blue planet

jay



On Jul 20, 2021, at 4:04 PM, Barton Churchill < 
[email protected]<mailto:[email protected]>> wrote:

If each lithium battery has an internal BMU and your wires are sized properly 
for their output it does not matter.
________________________________
From: RE-wrenches 
<[email protected]<mailto:[email protected]>>
 on behalf of Dave Angelini Offgrid Solar 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 20, 2021 4:02:20 PM
To: RE-wrenches 
<[email protected]<mailto:[email protected]>>
Subject: Re: [RE-wrenches] Lithium battery cable lengths



Seems wrong to me! The lengths need to be very close.  Why would you not
do this Jay?


Dave Angelini Offgrid Solar
"we go where powerlines don't"
https://us-west-2.protection.sophos.com?d=sti.net&u=aHR0cDovL21lbWJlcnMuc3RpLm5ldC9vZmZncmlkc29sYXIv&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=ZURpZGJ5TUxIbHJ6RnlSV1R6dVh6R2ZzMXM1dktRb2kxakRuQzRYa1hwMD0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=sti.net&u=aHR0cDovL21lbWJlcnMuc3RpLm5ldC9vZmZncmlkc29sYXIv&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=ZURpZGJ5TUxIbHJ6RnlSV1R6dVh6R2ZzMXM1dktRb2kxakRuQzRYa1hwMD0=&h=6f930d7a17ae43adac2b296e969243f1>
e-mail [email protected]<mailto:[email protected]>
text 209 813 0060

On Tue, 20 Jul 2021 14:58:10 -0600, Jay 
<[email protected]<mailto:[email protected]>> wrote:
> Hi all
>
> I’ve got a design for a lithium battery that has a 12’ longer run from
> furthest battery vs closer battery. 6 batteries in all. So lengths go
from
> 0-12’ plus to the combiner/ disconnect.
>
> What is the feeling about running different lengths vs making them all
the
> same length?
>
> How would this effect use of the batteries. Tech support has said no
> worries. Seems to me that physics says battery 1 gets more work than
> battery 6
>
> Thanks
>
> Jay
>
> Peltz power.
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: 
> https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3JlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=ZzJIYlNiOVpTSk1sdVJlYWs3Tk1hSWhlMC9yRjMyQjN1LzZEOE9Pa3drZz0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL3JlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=ZzJIYlNiOVpTSk1sdVJlYWs3Tk1hSWhlMC9yRjMyQjN1LzZEOE9Pa3drZz0=&h=6f930d7a17ae43adac2b296e969243f1>
>
> List Address: 
> [email protected]<mailto:[email protected]>
>
> Change listserver email address & settings:
> https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9vcHRpb25zLmNnaS9yZS13cmVuY2hlcy1yZS13cmVuY2hlcy5vcmc=&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=NVlGNklPMUN2VEVKcE9jTmhpWUp0TlE4Z25QeU00OEZTRjdVVWdKTlJ4dz0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9vcHRpb25zLmNnaS9yZS13cmVuY2hlcy1yZS13cmVuY2hlcy5vcmc=&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=NVlGNklPMUN2VEVKcE9jTmhpWUp0TlE4Z25QeU00OEZTRjdVVWdKTlJ4dz0=&h=6f930d7a17ae43adac2b296e969243f1>
>
> There are two list archives for searching. When one doesn't work, try
the
> other:
> https://us-west-2.protection.sophos.com?d=mail-archive.com&u=aHR0cHM6Ly93d3cubWFpbC1hcmNoaXZlLmNvbS9yZS13cmVuY2hlc0BsaXN0cy5yZS13cmVuY2hlcy5vcmcv&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=MlBMN0J6U2tRb0FVMzVaNnhQY3M0cUtrZGtvQUY4bGZlNDFQaE55MXJ6ND0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=mail-archive.com&u=aHR0cHM6Ly93d3cubWFpbC1hcmNoaXZlLmNvbS9yZS13cmVuY2hlc0BsaXN0cy5yZS13cmVuY2hlcy5vcmcv&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=MlBMN0J6U2tRb0FVMzVaNnhQY3M0cUtrZGtvQUY4bGZlNDFQaE55MXJ6ND0=&h=6f930d7a17ae43adac2b296e969243f1>
> https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9waXBlcm1haWwvcmUtd3JlbmNoZXMtcmUtd3JlbmNoZXMub3Jn&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=aitoQS9lbGs5WDhENWQrak90elRmS0lVN0c4ZFlHZjhSUEFTR3BUZG81RT0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9waXBlcm1haWwvcmUtd3JlbmNoZXMtcmUtd3JlbmNoZXMub3Jn&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=aitoQS9lbGs5WDhENWQrak90elRmS0lVN0c4ZFlHZjhSUEFTR3BUZG81RT0=&h=6f930d7a17ae43adac2b296e969243f1>
>
> List rules & etiquette:
> https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3d3dy5yZS13cmVuY2hlcy5vcmcvZXRpcXVldHRlLmh0bQ==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=UDlGR0Z4V0pESm1hQ2dHOGZvTkVPZHIySElRRDV1cWx2RHcwUFZtWG1TRT0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL3d3dy5yZS13cmVuY2hlcy5vcmcvZXRpcXVldHRlLmh0bQ==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=UDlGR0Z4V0pESm1hQ2dHOGZvTkVPZHIySElRRDV1cWx2RHcwUFZtWG1TRT0=&h=6f930d7a17ae43adac2b296e969243f1>
>
> Check out or update participant bios:
> https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3d3dy5tZW1iZXJzLnJlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=WUVqU0NLSDVVeHd5Ujk5aG8zR0lqMmZoTHRaZHNWM0lGQlB2d1RVaVc1az0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL3d3dy5tZW1iZXJzLnJlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=WUVqU0NLSDVVeHd5Ujk5aG8zR0lqMmZoTHRaZHNWM0lGQlB2d1RVaVc1az0=&h=6f930d7a17ae43adac2b296e969243f1>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: 
https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3JlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=ZzJIYlNiOVpTSk1sdVJlYWs3Tk1hSWhlMC9yRjMyQjN1LzZEOE9Pa3drZz0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL3JlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=ZzJIYlNiOVpTSk1sdVJlYWs3Tk1hSWhlMC9yRjMyQjN1LzZEOE9Pa3drZz0=&h=6f930d7a17ae43adac2b296e969243f1>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9vcHRpb25zLmNnaS9yZS13cmVuY2hlcy1yZS13cmVuY2hlcy5vcmc=&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=NVlGNklPMUN2VEVKcE9jTmhpWUp0TlE4Z25QeU00OEZTRjdVVWdKTlJ4dz0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9vcHRpb25zLmNnaS9yZS13cmVuY2hlcy1yZS13cmVuY2hlcy5vcmc=&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=NVlGNklPMUN2VEVKcE9jTmhpWUp0TlE4Z25QeU00OEZTRjdVVWdKTlJ4dz0=&h=6f930d7a17ae43adac2b296e969243f1>

There are two list archives for searching. When one doesn't work, try the other:
https://us-west-2.protection.sophos.com?d=mail-archive.com&u=aHR0cHM6Ly93d3cubWFpbC1hcmNoaXZlLmNvbS9yZS13cmVuY2hlc0BsaXN0cy5yZS13cmVuY2hlcy5vcmcv&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=MlBMN0J6U2tRb0FVMzVaNnhQY3M0cUtrZGtvQUY4bGZlNDFQaE55MXJ6ND0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=mail-archive.com&u=aHR0cHM6Ly93d3cubWFpbC1hcmNoaXZlLmNvbS9yZS13cmVuY2hlc0BsaXN0cy5yZS13cmVuY2hlcy5vcmcv&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=MlBMN0J6U2tRb0FVMzVaNnhQY3M0cUtrZGtvQUY4bGZlNDFQaE55MXJ6ND0=&h=6f930d7a17ae43adac2b296e969243f1>
https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9waXBlcm1haWwvcmUtd3JlbmNoZXMtcmUtd3JlbmNoZXMub3Jn&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=aitoQS9lbGs5WDhENWQrak90elRmS0lVN0c4ZFlHZjhSUEFTR3BUZG81RT0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9waXBlcm1haWwvcmUtd3JlbmNoZXMtcmUtd3JlbmNoZXMub3Jn&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=aitoQS9lbGs5WDhENWQrak90elRmS0lVN0c4ZFlHZjhSUEFTR3BUZG81RT0=&h=6f930d7a17ae43adac2b296e969243f1>

List rules & etiquette:
https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3d3dy5yZS13cmVuY2hlcy5vcmcvZXRpcXVldHRlLmh0bQ==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=UDlGR0Z4V0pESm1hQ2dHOGZvTkVPZHIySElRRDV1cWx2RHcwUFZtWG1TRT0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL3d3dy5yZS13cmVuY2hlcy5vcmcvZXRpcXVldHRlLmh0bQ==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=UDlGR0Z4V0pESm1hQ2dHOGZvTkVPZHIySElRRDV1cWx2RHcwUFZtWG1TRT0=&h=6f930d7a17ae43adac2b296e969243f1>

Check out or update participant bios:
https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3d3dy5tZW1iZXJzLnJlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=WUVqU0NLSDVVeHd5Ujk5aG8zR0lqMmZoTHRaZHNWM0lGQlB2d1RVaVc1az0=&h=6f930d7a17ae43adac2b296e969243f1<https://us-west-2.protection.sophos.com/?d=re-wrenches.org&u=aHR0cDovL3d3dy5tZW1iZXJzLnJlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=WUVqU0NLSDVVeHd5Ujk5aG8zR0lqMmZoTHRaZHNWM0lGQlB2d1RVaVc1az0=&h=6f930d7a17ae43adac2b296e969243f1>












































































_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: 
http://re-wrenches.org<https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3JlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=ZzJIYlNiOVpTSk1sdVJlYWs3Tk1hSWhlMC9yRjMyQjN1LzZEOE9Pa3drZz0=&h=c7afd09e373c487a8c108f4efef183d9>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9vcHRpb25zLmNnaS9yZS13cmVuY2hlcy1yZS13cmVuY2hlcy5vcmc=&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=NVlGNklPMUN2VEVKcE9jTmhpWUp0TlE4Z25QeU00OEZTRjdVVWdKTlJ4dz0=&h=c7afd09e373c487a8c108f4efef183d9>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/<https://us-west-2.protection.sophos.com?d=mail-archive.com&u=aHR0cHM6Ly93d3cubWFpbC1hcmNoaXZlLmNvbS9yZS13cmVuY2hlc0BsaXN0cy5yZS13cmVuY2hlcy5vcmcv&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=MlBMN0J6U2tRb0FVMzVaNnhQY3M0cUtrZGtvQUY4bGZlNDFQaE55MXJ6ND0=&h=c7afd09e373c487a8c108f4efef183d9>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL2xpc3RzLnJlLXdyZW5jaGVzLm9yZy9waXBlcm1haWwvcmUtd3JlbmNoZXMtcmUtd3JlbmNoZXMub3Jn&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=aitoQS9lbGs5WDhENWQrak90elRmS0lVN0c4ZFlHZjhSUEFTR3BUZG81RT0=&h=c7afd09e373c487a8c108f4efef183d9>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3d3dy5yZS13cmVuY2hlcy5vcmcvZXRpcXVldHRlLmh0bQ==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=UDlGR0Z4V0pESm1hQ2dHOGZvTkVPZHIySElRRDV1cWx2RHcwUFZtWG1TRT0=&h=c7afd09e373c487a8c108f4efef183d9>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://us-west-2.protection.sophos.com?d=re-wrenches.org&u=aHR0cDovL3d3dy5tZW1iZXJzLnJlLXdyZW5jaGVzLm9yZw==&i=NWY3Yjg4NTEwMTMzZWYwZjc4ZDZiZjM0&t=WUVqU0NLSDVVeHd5Ujk5aG8zR0lqMmZoTHRaZHNWM0lGQlB2d1RVaVc1az0=&h=c7afd09e373c487a8c108f4efef183d9>























_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to