Wrenches
Per request from Unirac I cut sections off and sent it back to unirac and
they say that modules that did not come loose we over tightened, they do
something like magaflux on iron, they could see fractures in the rails,
aluminum cracks when bent where steel is bending.
Jerry


On Tue, Sep 7, 2021 at 4:30 AM Will White <[email protected]> wrote:

> Jerry,
>
> I'm curious, how did they prove over torquing? When doing inspections it's
> easy to find connectors that are under torqued but I haven't heard of a
> reliable way to check for over torque.
>
> Thanks,
> Will
>
> On Mon, Sep 6, 2021 at 1:34 AM Jerry Shafer <[email protected]>
> wrote:
>
>> 1/4" x 20 is no more the 10 ftlbs (120 inlbs) and a good 1/4" impact
>> should be able to get you over 30 ftlb. When you overtorq bolts and nuts
>> you put undue and irreversible stretching and or tearing of the material
>> not to mention warping or bending of the plates, and rails, loosening and
>> retorqing is a wait as if damage is done its done, the best solution is to
>> replace all the stressed hardware. I have seen unirac "T" bolts crack the
>> the rails with a bad result, so the question is how far do you want to dig
>> and risk to take. Regarding cracked glass, I have only seen this with
>> incorrect use of the clamps but over torqing will also crush the frames. I
>> have inspected arrays after high wind events that resulted in destruction
>> of the array and the manufacture in all cases used over torq as thier out
>> so warranty are only as good as the installers.
>> Jerry
>> NABCEP PV inspector
>>
>> On Sun, Sep 5, 2021, 8:56 PM Corey Shalanski <[email protected]> wrote:
>>
>>> August,
>>>
>>> Thanks for your feedback.The racking model is EcoFoot2+
>>> <https://ecolibriumsolar.com/ecofoot2plus/> by Ecolibrium Solar (now
>>> part of Unirac). These module clamps are also self-grounding with teeth to
>>> bite into the module frame. I reached out to the manufacturer, who
>>> confirmed that the clamp material is aluminum extrusion and the hardware is
>>> stainless steel.
>>>
>>> The modules were installed about 2 weeks ago, so not very much time has
>>> elapsed to be able to observe potential resultant damage. We haven't seen
>>> any problems so far.
>>>
>>> --
>>> Corey
>>>
>>>
>>> On Fri, Sep 3, 2021 at 6:35 AM August Goers <[email protected]> wrote:
>>>
>>>>
>>>> Hi Corey -
>>>>
>>>> For many years we used Pro Solar racking and Unirac Solarmount and
>>>> tightened the clamps with impact drivers. At some point maybe roughly 8
>>>> years ago, Unirac switched its mid clamps to stainless steel self grounding
>>>> clamps with teeth to bite into the module frame. We continued to use
>>>> impacts with no issue. Then, starting around 4 years ago, we started to
>>>> have module glass failures with our SunPower commercial systems and these
>>>> Unirac clamps. We immediately switched to torque wrenches for tightening
>>>> the clamps. However, the failures continued. My guess is that the poor
>>>> design of the Unirac mid clamps in conjunction with thinner “weaker” module
>>>> frames exasperated the issue. We now have stopped using those mid clamps
>>>> and continue to hand tighten all clamps. We primarily install SunPower, and
>>>> their residential module frames have a lip so all the pressure from the
>>>> clamp doesn’t go to the glass.
>>>>
>>>> Getting to your question - what kind of mid clamps do you have? If they
>>>> are aluminum, there may be less risk than the stainless clamps. I would be
>>>> worried that the process of loosening and then re-tightening might cause
>>>> more damage than good if there aren’t any problems that have occurred to
>>>> date. It’s a good question.
>>>>
>>>> August
>>>> Luminalt
>>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to