Hello Sir The FM100AFCI will need to paired up with a Mate3S. The FM100 has on board ground Fault Detection so the GFDI used with the FM60/80 is not required Please see page 13 in the manual below. https://outbackpower.com/downloads/documents/charge_controllers/flexmax_100_afci/fm100_afci_manual.pdf There are 300 vdc rated breakers available due to the higher dc voltages possible on the array. The breaker part numbers are listed on page 15 in the above manual. I hope this helps. Take Care and Stay Safe
-----Original Message----- From: RE-wrenches <[email protected]> On Behalf Of Jesse Dahl Sent: Tuesday, September 7, 2021 12:02 PM To: Wrenches <[email protected]> Subject: [RE-wrenches] FLEXmax 100 CAUTION: This email originated from outside of the Company. Do not click links or open attachments unless you recognize the sender and know the content is safe. Hi. We have a 24V bi-modal outback system that run the residential wiring labs for the electrical program I teach. Long story short, the FM60 we are currently using had an operator error and we need to get a new charge controller. Can the FM100 Work “seamlessly” with an older outback systems? Wire sizes and array sizes all work out according to the data sheets and documents I’ve read. Is there any unforeseen issues with the MATE3 or optics RE that would come up if we upgrade to the 100? The Higher array VOC for the 100 will make the labs easier to set up, that’s why I’d like to get the 100. Thanks, Jesse Sent from my iPhone _______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: https://protect2.fireeye.com/v1/url?k=342a0c9f-6bb13449-34290514-86ae1f962b30-439262079b22cd5c&q=1&e=6969e4fc-681b-4a2e-a8f4-1a337b4f9a50&u=http%3A%2F%2Fre-wrenches.org%2F List Address: [email protected] Change listserver email address & settings: https://protect2.fireeye.com/v1/url?k=4f57ff66-10ccc7b0-4f54f6ed-86ae1f962b30-5667499a2be9e892&q=1&e=6969e4fc-681b-4a2e-a8f4-1a337b4f9a50&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ https://protect2.fireeye.com/v1/url?k=fbb57e29-a42e46ff-fbb677a2-86ae1f962b30-eae306de7fc53f7e&q=1&e=6969e4fc-681b-4a2e-a8f4-1a337b4f9a50&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org List rules & etiquette: https://protect2.fireeye.com/v1/url?k=cc2da448-93b69c9e-cc2eadc3-86ae1f962b30-8ffc6f3bfd79e1c5&q=1&e=6969e4fc-681b-4a2e-a8f4-1a337b4f9a50&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm Check out or update participant bios: https://protect2.fireeye.com/v1/url?k=cc59b181-93c28957-cc5ab80a-86ae1f962b30-a3fea6b17cdd3aa3&q=1&e=6969e4fc-681b-4a2e-a8f4-1a337b4f9a50&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F This email and any attachments may contain confidential information that is intended only for the recipient(s). If you have received this email in error, please notify the sender and delete it from your system. Any views or opinions presented in this email are solely those of the author and do not necessarily represent those of the company or its affiliates. This email does not constitute an agreement to conduct transactions by electronic means and does not create any legally binding contract or enforceable obligation in the absence of a fully signed written contract. The recipient should check this email and any attachments for viruses. The company accepts no liability for any loss or damage caused by software viruses. If you are the intended recipient and you do not wish to receive similar email(s) from us in the future then please notify the sender. Please consider the environment before printing. _______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org