I've got some old systems running the QO breakers at 48 v nominal, but the Voc of the array could be over 80.  Never an issue, but I agree just swap out that load center, since its that old.  Midnite has good stuff.  If you're just running to a an FM80 or similar with 150 v limit, their regular breakers are 150 vdc rated. I only use the 300 v rated breakers with the new FM 100 that can take 300 vdc.

Ray Walters
Remote Solar

On 10/25/2021 6:45 PM, Chris Sparadeo wrote:
Hi Jeremy,

According to the QO cut sheet the answer is 48VDC:

https://download.schneider-electric.com/files?p_Doc_Ref=0730CT9801

My guess is that your string voltage would be much greater than that. Not sure your exact application, but for the slight added cost, I would definitely suggest using a reputable NEMA3R combiner/disco with 300VDC breakers and throwing away the ancient load center.




On Mon, Oct 25, 2021 at 8:30 PM Jeremy Rodriguez <[email protected]> wrote:

    Hello
    Does anyone have a definitive answer to the DC rating of the QO
    circuit breakers?   I’ve got a potential client with an existing
    AC load center (>20 yrs) being used for his array combiner.
    He’s looking to add to the array, with modules that are higher
    voltage of course.
    Thanks in advance.

    Jeremy Rodriguez
    Solar Installation / Design Expert
    All Solar, Inc.
    1453 M St
    Penrose Colorado 81240

    Sent by Jeremy's iPhone. Sorry for typos and shorthand.
    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

--
Chris Sparadeo


C_802-369-4458
H_802-728-3059

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to