Hi Dan

As it works with a manual start, I have to ask about the ags settings. 

All start parameters that you want to use need to be manually  enabled:  volts 
( 24, 2hr, 2 min) load ( start/stop kW) and SOC.

Is the quiet time enabled?  If so is the date and time been updated to correct 
local time?

I’ve had very good luck with OB AGS especially with mate 3/3S. 

Curious what you find

Jay





> On Jan 7, 2022, at 3:02 PM, Dan Fink <[email protected]> wrote:
> 
> 
> Wrenches; Having a frustrating problem here with a Mate 3s and 2-wire AGS. 
> The generator starts and stops fine from the Mate 3 AND via Optics RE from my 
> smartphone,  but will not autostart by either SOC or Voltage. It is wired to 
> use the inverter (VFXR 3524A) 12vdc aux output to an Outback relay board in 
> the gen  as I've had issues in the past using the FNDC relay (as I think 
> other Wrenches have too). The Mate 3s AGS is set for the Inverter port (4).
> 
> In the past on other Mate 3s systems, I seem to remember always making sure 
> the Inverter AUX relay mode is set to REMOTE to allow the Mate 3s to control 
> the gen instead of the very limited GEN FAULT AGS setting in the inverter. 
> But when I pull that up both via Optics and the Mate 3s itself, there IS no 
> "remote" option anymore. The Mate3s firmware was updated last month to the 
> latest version. 
> 
> If the REMOTE setting for the VFXR inverter no longer exists, what do I set 
> the inverter AUX relay for to enable the Mate 3s advanced AGS to assume 
> control? Or should I delegate AGS responsibilities to one of the FX PV 
> controllers , just re-routing the 2 genstart wires? Not to the FNDC I assume 
> because of those past problems.
> 
> I'm pretty sure this issue has to be conflicting AGS instructions from 
> different components, as sitting here at the kitchen table at the client's 
> off grid house I can start and stop the gen from my phone! 
> 
> Thanks for any suggestions!
> 
> Dan Fink
> Buckville Energy Consulting LLC
> 970-672-4342
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to