That's a long enough run that you really need to weigh the cost of a separate system.  I'm not seeing the advantages of keeping a single system for the whole island.

Ray Walters
Remote Solar
303 505-8760

On 1/10/22 9:43 AM, Chris Mason wrote:
I would use a 6,600V single phase outdoor pad mounted transformer pair and deep bury a single #2 direct burial cable. Easy and quick.

On Mon, Jan 10, 2022 at 7:34 AM Foxfire Energy <[email protected]> wrote:

    Hi Guys, Got a good one for you.. We were tasked to refurbish a
    Stand Alone (aka Off Grid) power system on a 100 acre private
    resort island off the New England coast a few years back.. The
    system has a 12kW(AC)/ 48VDC power center (@120/240VAC) with a
    10kW Bergey wind turbine, 3kW of Solar and a 12kW Diesel
    Generator.. It currently powers two main lodges and 10 private
    cabins.. The system was never installed properly and had
    significant damage when we got there (no system ground, evidence
    of several lightening strikes, open/corroded connections, and poor
    workmanship in general)
    The new owners want to build a third lodge at the other end of the
    island.. Some 3600ft away, and want to feed full power from the
    existing system to the new lodge.. Thing is, the new owner is
    pretty brainy (keeps me on my toes).. My first thought was to bump
    the 120/240VAC up to 480VAC and send it on like 4/0AL and back
    down to 120/240VAC at the new lodge (we've done it before).. The
    new owner wants to launder the AC to DC and back for
    transmission.. Says DC for transmission is the new Cats Pajamas
    because of the efficiency.. News to me.. Anyone have experience
    with DC for transmission? Again.. I'm shooting for 15kW (including
    25% for continuous duty), 3600ft, 600V wire (but could go with a
    different wire) and a line loss under 5%. TIA db

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org



--
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to