Friends:


I am sure many of you are familiar with the somewhat new Outback FM100
charge controller.  It allows PV input at up to 300 volts and battery feed
at up to 100 amps.  It has a built in GFDI fuse, much like the old XW--now
branded I think Conextant-- charge controller.



Outback recommends against installing an FM 100 in an installation with
FM60s or FM 80s.  Here is the tech note
<https://outbackpower.com/downloads/documents/appnotes/fm100_fm80_app_note.pdf>
that gives that recommendation.  Below is one paragraph from that tech note.



*There is little benefit to mixing an FM100 with an FM60/80. If
circumstances require it, this application*

*note will explore an option.*



Note the language is pretty dang squirrely.  Let’s parse the above
paragraph:



Sentence 1:  I submit there may be many scenarios where there is
significant benefit:  Like if you already have an FM60/80 and you want to
add more PV and you want to enjoy the benefits of an FM100, such as higher
input voltage or higher output amperage, and not have to fork out an extra
$1000 to replace a working FM60/80.  Or you installing more than one PV
array,  one array nearby and/or smaller and one further away or larger, and
you don’t want to spend close to $1,000 to charge control the nearer array.



Sentence 2:  They are offering “an option,” not the only option.  I believe
there are multiple options. In a mixed installation, the FM100 can rely on
its internal GFDI fuse and the FM60 or 80 can rely on the old familiar GFDI
breaker with the 1 or 0.5 amp pole connected between the negative and
equipment grounding system.  Alternatively, Midnite sells a 300 volt rated,
multi-pole GFDI breaker that could be shared by an FM100 and an F60/80.  It
says right in the FM100 manual that you can use external GFDI devices (page
14).



I am not at all clear as to what problem there is to mixing the two
generations of charge controllers.  I reviewed the NEC.  There is no
indication that thou shall not mix GFDI styles.



If anyone has a definitive reason why or why not to mix these models of
Outback charge controllers, I would be most interested.



Most Sincerely,



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to