Just a rated disco at the ground mount?   Labeled as the rapid shutdown switch?
That’s  too simple!

In

Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand.

On Feb 1, 2022, at 6:49 PM, Lloyd Hoffstatter <[email protected]> 
wrote:


We’ve used multi-pole rated disconnects at the array.
Best regards,
Lloyd

Lloyd Hoffstatter
Sunstruck Consulting

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: RE-wrenches <[email protected]> on behalf of 
Jeremy Rodriguez <[email protected]>
Sent: Tuesday, February 1, 2022 8:31:16 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems

What about the PV circuits that leave the combiner and are ran on or in a 
building to the CC



Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand.

On Feb 1, 2022, at 4:07 PM, Brian Mehalic <[email protected]> wrote:

 For a ground mount PV system with a DC combiner, the PV source circuits are 
not in or on a building so RS doesn’t apply to them. And the definition of a 
charge controller in Art. 100 is in its relationship to batteries/storage, not 
really the charging source - fundamentally it’s there to protect the 
storage/batteries, so it’s best considered part of that system, not the PV 
system (and over the last several cycles nearly all references to charge 
control/lers have been moved out of 690).





Brian

On Feb 1, 2022, at 3:15 PM, Bradley Bassett <[email protected]> wrote:


"A switch, outside of the building, opening the PV circuit to the power 
electronics, and functioning as the pv system disco and the rapid shutdown 
initiation device, should be all that is required."

That is what I have found most inspectors will accept, but not all. A strict 
reading of the code does come to the same conclusion that William comes to, and 
some inspectors will require that. The code is not very specific on where the 
PV system disconnect should go. It seems to be mostly accepted to be on the PV 
side of the charge control, but when I read the code strictly it seems to me it 
should be on the battery side of the charge control since it is only a PV 
device. Fortunately the PV side is more accepted because that makes things much 
easier.

What I'm still having trouble with is the requirement for breaking both pos and 
neg legs in the PV system disconnect unless solidly grounded which most systems 
are not (690.13(E)). I see that most installers do not break both poles, but 
only the positive leg, which is of course easier and less expensive. I've 
quoted the use of dual pole breakers when possible, but OutBack does not really 
call for that always, and if you ask about their 2 pole 300V breakers they (and 
Carling) don't say they can be used that way. And if you do, you have to run 
the wires in opposite directions for polarity. I've asked for clarification but 
have not received it yet. Then there are the high voltage charge controls like 
Schneider, where often one uses the SqD HU361, which can be wired in various 
ways to meet the 600V requirement. It can be wired one pole for up to 18A Isc 
for PV, or up to 30A if two poles in series, or one pos and one neg pole in the 
circuit. The Schneider RS Disco does break both poles, one of the few devices 
that make it clear. I'm curious what others are doing.

Brad

On Tue, Feb 1, 2022 at 11:23 AM Brian Mehalic 
<[email protected]<mailto:[email protected]>> wrote:
Sorry, forgot to state my previous comment was in regards to a ground-mount.

Brian

On Feb 1, 2022, at 12:19 PM, William Miller 
<[email protected]<mailto:[email protected]>> wrote:



Ray:



Thanks for that input.  I was hoping I was wrong.  I looked for that discussion 
in the archives but could not find it.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com<http://www.millersolar.com/>

CA Lic. 773985





From: RE-wrenches 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Ray
Sent: Tuesday, February 1, 2022 10:11 AM
To: [email protected]<mailto:[email protected]>
Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems



 Ground mounts do NOT require RSS.  We hashed this out years ago on the 
Wrenches list, when NEC 2017 came out.

See Figure 690.1(B) Note (2): " The PV system disconnect in these diagrams 
separates the PV system from all other systems".

Thus, the PV disconnect is defined as the transition point from the PV system 
to all other systems, like battery or inverter systems. The installer/ designer 
decides where to put that disconnect.  I usually put it on the wall before it 
goes into the building, and I have never had an inspector question that.

Thanks,

Ray Walters

Remote Solar

303 505-8760

On 2/1/22 10:06 AM, William Miller wrote:

Jay:



Here is the text from 2017:



690.12 Rapid Shutdown of PV Systems on Buildings. PV

system circuits installed on or in buildings shall include a rapid

shutdown function to reduce shock hazard for emergency

responders in accordance with 690.12(A) through (D).



Exception: Ground mounted PV system circuits that enter buildings, of

which the sole purpose is to house PV system equipment, shall not be

required to comply with 690.12.



The wording is interesting.  The requirement is directed at “PV system 
circuits…”, not PV arrays.  The passage does not specify where the PV feeding 
those circuits is located, it just addresses where the circuits are, 
specifically “in or on a building.”



The only circuits that are exempt are those feeding a building that serves only 
one purpose, to house PV equipment.  For circuits that enter building with 
other uses—homes, garages, barns, workshops, etc.-- it would seem there is a 
requirement to have rapid shutdown systems (RSS).



Reading through the rest of the section, I don’t see any language that gets us 
out of the requirement to reduce voltages to less than 80 volts within 30 
seconds inside the array boundary, as in module level shutdown, regardless of 
roof-top or ground-mount.  Although the 2020 code includes some differing 
language, I don’t see it as exempting ground mount systems.



The moral of the story is this:  For ground-mounts:  either install RSS or put 
your equipment (inverters, charge controllers, batteries, BOS) in a separate 
building housing only that equipment.



I don’t necessarily like the requirement, but I think it exists.  Jay, or 
anyone, please, please tell me I am reading this incorrectly.



By the way, regarding battery circuits, here is a quote from a post by Bill 
Brooks on March 16, 2016:



In the 2017 NEC, we were very careful to carve out all batteries and loads,

that were previously part of PV systems, and place them in their own

articles.



I have not read through the battery sections of the code to verify this, I am 
taking Bill at his word.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com<http://www.millersolar.com/>

CA Lic. 773985





From: Jay [mailto:[email protected]<mailto:[email protected]>]
Sent: Tuesday, February 1, 2022 6:07 AM
To: [email protected]<mailto:[email protected]>; RE-wrenches
Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems



2017 code has a specific exception/clarification for ground mount solar that it 
does not need RS.

It’s in the first line after 690.12



Jay



On Feb 1, 2022, at 12:13 AM, William Miller 
<[email protected]<mailto:[email protected]>> wrote:



Jerry:



Yes it is required.  Rapid Shutdown:  NEC 690.12.  All buildings except 
dedicated solar buildings.  Read it and weep.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com<http://www.millersolar.com/>

CA Lic. 773985





From: Jerry Shafer 
[mailto:[email protected]<mailto:[email protected]>]
Sent: Monday, January 31, 2022 7:21 PM
To: William Miller; RE-wrenches
Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems



William

Are you sure RSD is required on a non habitable building, historically its not 
required. Now that being said we use fire raptor with the best results, yes it 
takes an extra conduite and might require a button and power supply depending 
on inverter application.

Jerry



On Mon, Jan 31, 2022, 9:57 AM William Miller 
<[email protected]<mailto:[email protected]>> wrote:

Friends:



It is quite rare for us to install off-grid systems on roof-tops.  We have one 
coming up with about 20kW on a large barn roof.  This will be our first 
off-grid with a module-level rapid shutdown requirement.  I see no exemptions 
from RSS for off-grid systems in the code.  I have looked at the options and 
this is what I have found:



1.   Fire Raptor

2.   Tigo TS4-F

3.   AC coupling with micro-inverters or optimizers



No one of these approaches seems ideal.  The fire raptor requires extra wiring 
for control leads.  The Tigo requires a wireless control system which worries 
me about reliability.  With AC Coupling systems floating the proposed AGM 
batteries may be awkward.  Furthermore, with AC coupled systems one cannot 
charge batteries unless the mini-grid is operational, a big problem.



Have any of you implemented module-level RSS on a battery-based inverter 
system?  I looked in the archives and found no threads that apply.  Thank in 
advance.



William Miller







_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to