Bill,

This was the subject of a thread last year on this forum.  Briefly- we had a 
very negative experience with APSmart RSD last year.  SMA inverter threw all 
sorts of weird errors after about a week of normal operation.  It would operate 
normally if a hard reset was preformed each morning.  Spent many hours on SMA 
tech support calls. Changed inverter, problem persisted.  We then attempted to 
get support from APSmart in concert with SMA level 2 folks, but very high 
language barrier and zero accountability - we purchased their high output 
signal device and spent time installing that even though we had a good RSD 
signal from the inverter.  We checked every connection, wire, panel, etc and 
found nothing.  Eventually, inverter threw an arc fault code so We went back up 
on roof, removed panels and found that one of the APSmart RSD’s had essentially 
exploded. There was molten plastic on the roof, a big flame mark under 2 panels 
and on the roof.  Thankfully, it was a metal roof with no leafy materials so 
911 wasn’t called!  Bottom line, I won’t ever be using their equipment agin.  
They completely failed to understand the magnitude of this failure, which is 
what bothered me the most.  The customer lost all faith in going solar and was 
on the brink of asking us to remove the system. We lost money and a lot of good 
referrals on that job. So yeah, I’m NOT a fan.

 Hopefully you’ll be able to see this pic:

Jeremy Coxon NABCEP 
Certified MWBE

Sent from my iPhone

> On Feb 8, 2022, at 10:20 AM, frenergy <[email protected]> wrote:
> 
> If an AP Smart fails does it sometimes or always take out the string.  And 
> how is it found in the string?  Any melted or near fire type failures out 
> there?
> 
> Bill
> 
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
> 
> 
> -- 
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
> 
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to