The VOC will start the microinverter, but I would pair a 365W module with
the IQ7+. It depends on where you are and how.much clipping there might be
based on temp, orientation, etc. But, the IQ7+ is now in short supply, so
you might want to look at the IQ8+.

I have never had an issue with a module voltage close to the microinverter
specified startup voltage.

Jason Szumlanski


On Wed, Apr 13, 2022, 4:56 PM Drake Chamberlin via RE-wrenches <
[email protected]> wrote:

> I'm concerned that a microinverter - module pair that has been specified
> by a supplier may not work. The maximum power voltage is very close to
> the minimum starting voltage. The Voc is adequately high.
>
> An Aptos DNA-120-MF26-365W is paired with an Enphase IQ 7A
>
> •       Minimum start voltage of the inverter is 33 V
> •       Vmmp of the module is 33.96 V
> •       Voc of the module is 40.7 V
>
> Is the 33 V starting voltage going to be a problem with a module STC Max
> power voltage of 33.96 V? Is it the Voc that determines the starting of
> the inverter or the Vmmp?
>
> Thanks,
>
> Drake
>
> Drake Chamberlin
> Athens Electric LLC
> Ohio Electrical Contractor’s License 44810
> CO Master Electrician’s License 4526
> NABCEP Certified PV Installation Professional
>
>
> --
> _______________________________________________
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to