Hi, Ron, Yes, you must be careful of the MPPT inputs.  You state Sol-Ark
has an 18 amp max input, meaning you can not have more than 1 string
supplying an MPPT if your 60 cell modules are 10 amps Isc.  You state
Sol-Ark has a maximum voltage per MPPT of 500 volts, this voltage is *not
Voc x number of modules.*  The Voc must be temperature corrected.  find the
lowest temperature for your region, check code book 690.7a table and there
is a table of temperature correction factors, use these factors to correct
Voc at STC to Voc at your lowest temperature.   For example if your lowest
temp is -10 F the code says (x1.2) so your 40 volts becomes 40 x 1.2 = 48
volts and the max number of modules is 10 per string

On Tue, Apr 12, 2022 at 9:42 PM Ron Young via RE-wrenches <
[email protected]> wrote:

> Hi Wrenches, trying to wrap my head around a first time Sol-Ark install.
> Because the max DC voltage is 500v at 18a  and the PV I’m using is 40v DC
> each I will have to create three strings each 480v. What would be the best
> choice for a home run wire? I’ve always used smaller strings with micro
> inverters, a combiner at the array and a single Teck home run cable but the
> string inverter presents a different scenario and it looks like I’ll need
> to use three home run cables, one for each string.
>
> Ron Young
>
> earthRight Products - Solareagle.com
> Alternative Energy Solutions ~ Renewable Energy Products
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to