I want to comment, maybe without value.  The breaker you mention is called
a "shunt trip" breaker.  This is common type breaker in the electrical
industry.  The MN breaker has a 24 volt solenoid that trips the breaker.
Shunt Trip breakers have the solenoid voltage for the system voltage.  BUT
the way it works!! (load side of breaker is connected to one side of the
trip solenoid the other side is connected to switch and then to (neutral).
When the switch is closed current rushes through the solenoid, triping the
breaker stoping the solenoid current.  But what to do with solar
equipment?  Often when the bsttery is dis onnected the losd side of the
breaker does not go to neutral and the solenoid can carry current and will
fsil

On Mon, May 9, 2022, 7:43 PM Jeremy Rodriguez via RE-wrenches <
[email protected]> wrote:

> Does anyone have a solution for operating a remote trip MN battery breaker
> since the BDM is gone?
>
> We do have a birdhouse, so maybe someone has a BDM, but otherwise,
> what to do?
>
> Batteries in a dwelling
>
>
> Jeremy Rodriguez
> Solar Installation / Design Expert
> All Solar, Inc.
> 1453 M St
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to