Having witnessed the aftermath of others who have installed batteries by 
bolting brackets to wood stud walls, my advice is do not do it! You reinforce 
the structure prior to mounting the batteries but failing to do could result in 
a catastrophic failure. When in doubt consult with your friendly local engineer 
who can properly evaluate your plans.

From: RE-wrenches <[email protected]> On Behalf Of 
James Jarvis via RE-wrenches
Sent: Tuesday, September 6, 2022 9:38 AM
To: RE-wrenches <[email protected]>
Cc: James Jarvis <[email protected]>
Subject: Re: [RE-wrenches] Discover AES Wall Mount Considerations

Buckling of the wall studs is most likely going to be the failure mode. You can 
use WebStructural to look at different designs. You'll find that accurately 
defining the constraints on the structural members is the most troublesome.
https://webstructural.com/

Personally, I don't think that supporting a couple of thousand pounds of dead 
load hanging off the sides of $2 studs fastened with unknown fasteners into 
unknown top and bottom plates is a super great idea. I would do it on a poured 
concrete wall, but this sounds like it is asking for trouble.


-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
http://www.aprsworld.com/


On Tue, Sep 6, 2022 at 9:30 AM Jason Szumlanski via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
2x4 studs have compressive force to hold up over 1,000 pounds each when 
constructing a load bearing wall, so I don't think that is a limiting factor. 
But I am not a structural engineer, so consulting one would not be a bad idea.


Jason


On Tue, Sep 6, 2022, 10:21 AM Chris Sparadeo 
<[email protected]<mailto:[email protected]>> wrote:
Thanks Jason,

I’m still wondering if there is an IBC reference for weight. The Discover 
manual only states:

“ For structural and seismic stability, the AES Battery must be mounted onto a 
vertical supporting surface strong enough to support a minimum of 227 kg (500 
lbs) per battery. Failure to follow these instructions can result in death or 
serious injury.”

Other than asking a structural engineer, how can I be sure that the wall is 
rated to 4,500 lbs?

On Tue, Sep 6, 2022 at 9:20 AM Jason Szumlanski via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
That won't be a problem as long as they are spread across several studs. Even 
2x4 studs would be fine. Check the installation manual for details. The shear 
and pull out strength of the fasteners will be the limiting factor, not the 
wall itself unless very poorly constructed.

https://assets.discoverbattery.com/documents/03_aes/805_product_manual/gui-aes-wall-mount-bracket-installation-guide.pdf

Jason Szumlanski
Florida Solar Design Group



On Tue, Sep 6, 2022, 8:59 AM Chris Sparadeo via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Hi all,

I have a project where I am contemplating hanging 9 Discover AES batteries on a 
wall. Each battery is around 200 lbs, and although the stud wall is a bulky 
2”x6” with 16” OC…I have apprehensions that hanging almost a ton of battery on 
the wall is a good idea. I’ve seen it done in other install photos, however I 
can’t seem to find and good building code that would inform my decision.

Does anyone out there have a building code reference or experience that might 
help?

Thanks!

-Chris
--
Chris Sparadeo


C_802-369-4458
H_802-728-3059
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
--
Chris Sparadeo


C_802-369-4458
H_802-728-3059
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to