That’s a market segment that no inverter company that I know of really makes a 
product for. 
I would probably use 3 Sol-Ark 12K inverters. 
You’ll have to be careful with load balancing with any Sol-Ark inverter though. 
Schneider would also work but you will have a lot of individual components and 
you would need to be careful that the internal transfer switch is within its 60 
amp capacity limit from a generator or other source. With multiple Schneider 
inverters there is the possibility that not all of the internal transfer 
switches will  trip at exactly the same time causing the transfer switch in one 
inverter to take the whole load. 
I was originally a staunch Outback fan but we’ve stopped using their products 
after we had repeated Incidents of equipment not working right out of the box.  

Vince McClellan 
Energy Design 

> On Sep 8, 2022, at 07:30, Jerry Shafer via RE-wrenches 
> <[email protected]> wrote:
> 
> 
> Outback FX R can be built to be 3 phase and solark also works, for 30 k l 
> would look at solark, 3 12's or 15's.
> Jerry
> 
>> On Thu, Sep 8, 2022, 4:42 AM Mac Lewis via RE-wrenches 
>> <[email protected]> wrote:
>> Hello Wrenches,
>> 
>> What inverter options are there for 3 phase, UL listed, off-grid inverter 
>> systems in the 30kW+ category?  
>> It's been quite a while since I dove into this...
>> Thanks!
>> 
>> -- 
>> 
>> 
>> 
>> Mac Lewis
>> 
>> "Yo solo sé que no sé nada." -Sócrates
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to