I’ll usually use  a 60 amp contactor with 240Vac coil. 

The generator powers the coil and opens the Normally Closed contacts 
disconnecting the grid tie inverter. 

Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection 
[email protected]
512-460-9825


> On Oct 11, 2022, at 11:26 AM, Kirk Herander via RE-wrenches 
> <[email protected]> wrote:
> 
> Hi,
> I’m looking for suggestions on a remote control 60 amp contactor. It can 
> either be true wireless or send a signal down an AC power line to open / 
> close contact at the other end.
> 
> I’m trying to figure out a non-wired way to turn an AC coupled inverter off 
> when the generator is running, as advised by outback and others.
> 
> All suggestions welcome thank you.
> -- 
> Kirk Herander / [email protected]
> Owner|Principal, VT Solar, LLC
> Celebrating our 31st Anniversary 1991-2022!!
> www.vermont.solar
> dba Vermont Solar Engineering
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org