Hi Kris

What voltage do you have your charge settings at?  

I recommend that bulk or absorb voltage for lithium iron phosphate not be set 
above 56 V  - there is no reason for it even though many manufactures suggest 
higher settings.      In cases where total storage is sized generously enough I 
 often use 55.6 or even 55.4 in order to target 95% as full instead of 100% in 
order to extend cycle life.   and for float there’s no reason to ever go over 
54 V and better maybe even to be in the mid-53s. 

See if that helps assuming you had it higher. 

The other thought is you have one bms that is perhaps not protecting overcharge 
 and allowing a temporary spike when the others do limit. 

Hope that helps!  

Best Jeff C. 
Village Power Design



Sent from my iPhone

> On Nov 19, 2022, at 6:32 AM, Kristopher Schmid via RE-wrenches 
> <[email protected]> wrote:
> 
> 
> Greetings all,
> 
> I have seen an issue on two different systems that I am hoping someone can 
> shed some light on for me.  One was a 48 volt pack of 12 volt Battle Bornes 
> and the other was a 24 volt pack of SOKs.  What happens is when reaching the 
> end of the bulk charging stage, the battery voltage spikes and sends the 
> inverter into an overvoltage error.  Can anyone explain what is happening and 
> a solution?
> 
> Thanks,
> Kris
> 
> Shine On!
> 
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to