Dear Mike,

As co-author of upcoming book "The Handbook of Solar Water Pumping", we have 
expanded its definition to include micro and national grid-tied systems in 
which pumping is synchronized with power availability from PV. I had known 
about frequency-based load control for microgrids (from an SMA-based microgrid 
I toured in Israel). I had no idea it was a happening system on public grids 
until I read your response here. I love how it requires no communication lines 
or digital signals. It's a "natural" and logical concept from the old days of 
spinning generators under varying load.

I see your PG&E reference, but is there also a reference text you can recommend 
that I can use in the book as a universal explanation of how this works?  It 
can be SMA documentation, or other ref.  You can reply here if it's useful to 
the list, and/or contact me off-line.

Thanks!  – Windy

> On Dec 1, 2022, at 5:47 PM, [email protected] wrote:
> 
> From: Harry Mahon <[email protected] 
> <mailto:[email protected]>>
> Subject: Re: [RE-wrenches] AC Coupling Standard?
> Date: December 1, 2022 at 5:47:18 PM MST
> To: RE-wrenches <[email protected] 
> <mailto:[email protected]>>
> 
> 
> Definitely it is possible for newer grid-interactive inverters.  However, for 
> grid-tied operation, the utility that runs the grid sets the rules (and sets 
> the setpoints as it were), and it can be confusing....
>  
> Looking at PG&E’s Rule 21 tarriff (submitted Aug 12, 2022, effective Nov 4, 
> 2022) Freq-Watt reuirements are:
> “When system frequency exceeds 60.036 Hz, the active power output produced by 
> the Smart Inverter shall be reduced by 50% of real power nameplate rating per 
> hertz (5% of real power nameplate rating reduction per 0.1 hertz)”
> Bottom of Sheet 207 of : 
> https://www.pge.com/tariffs/assets/pdf/tariffbook/ELEC_RULES_21.pdf
>  
> So a 5kW inverter needs to ramp at 2.5kW/Hz.  But if it is only producing 
> 2.5kW, it has to be at 0W at 61.036Hz.....
>  
> Mike

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to