David:

I investigated a grid-connected SW system in 2017. There were no GTI units
in place. The sell function was disabled. The utility reported  that
back-feed was occurring.

Upon further investigation it turns out the SW inverters were selling about
1 amp 24/7. I can’t remember if it was 1 amp each or in total. Of course
this unexpected back-feed is not acceptable. It is possibly the cause of
the utility complaint in this case.

I believe the GTI units were invented to prevent this uncontrollable
back-feed.

I hope this information is helpful.

William Miller

On Mon, Dec 19, 2022 at 7:22 AM David Palumbo via RE-wrenches <
[email protected]> wrote:

> Wrenches,
>
>
>
> I have been retired from doing solar installs for 10 years now and I am
> reaching out for help as to recommending a solution to an old
> do-it-yourself customers question.
>
> His solar system that was formerly off-grid and is now using grid power
> instead of a back up generator.
>
> He had/has no intention of doing a net-metered system. Just trying to
> reduce dependance on a fossil fuel genset during our mostly sunless Vermont
> winters.
>
>
>
> He says that he brought in power a few years ago to run their expanding
> maple sugaring operation located next to their house. At that time they ran
> a 115Vac circuit (grid power) over to their house and connected grid power
> into AC Hot In terminal #! in their Trace SW 2512. This is correct as I see
> terminal #2 is labeled for generator power.
>
> He has the Trace programmed for float mode  not sell mode.
>
>
>
> Their local utility was working on the line nearby on the main road and
> noticed a small amount of current flowing into the grid and figured out
> where it was coming from. The utility did not immediately shut him down.
> Just told him to correct the problem. He is asking me for advice.
>
>
>
> My first inclination is to separate the grid power completely from the
> inverter power and to feed both power sources into a double pole double
> throw transfer switch. What other options should be considered.
>
>
>
> Thanks in advance and happy holidays,
>
>
>
> Dave Palumbo
>
> Formerly > Independent Power & Light
>
> Hyde Park, VT
>
> 802-371-8678 voice or text
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --

William Miller
Miller Solar.com
895-438-5600
www.millersolar.com
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other: