It can be done but it is not an easy job. You are 2 generations of XW back.

XW+ was good at this and XW pro was designed for this
along with being able to charge based on Soc (from the BMS) as well as voltage.

Is this an insured home? You might need a permit as this has to be legal for your area. Out west of you is what we do. Good Luck !

The main impact of Rule 21 for solar installers is that any of your installations in the state of California must now use Rule-compliant inverters. In effect, these are smart inverters that have been certified as UL 1741-SA or that are listed on the California Energy Commission's compliant inverter
 database.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  [email protected]
text 209 813 0060

On 2022-12-21 5:23 am, Jeremy Rodriguez via RE-wrenches wrote:

I've inherited a XW. 6048 system that we just installed a LiFePO4 battery bank with.
Has anyone successfully used Grid Support with Sell disabled?
This system never had an Interconnection Agreement with the utility co so it cannot sell.
Currently we have :
AC charger on , Multi Stage
PV input
Sell disabled
Grid Support disabled
There is no TOU metering.

Regards,

Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand.
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to