Hi john

Good to hear from you. 

Your system charges at above Outback programmed amp setpoints? 
And in a sort of cyclical way?  Sometimes it’s normal for an hour then will go 
to 2x charge rate then back down then maybe 1.5. 

I talked to a senior Outback tech and they haven’t heard of this issue. 

But if you say is true, how do you adjust the settings so it won’t trip the 
generator breaker?

This one is already at 5aac on ac input and 5 aac on charge and it will still, 
not often trip the generator breaker. 

Thx
Jay



> On Jan 3, 2023, at 8:13 PM, John Blittersdorf via RE-wrenches 
> <[email protected]> wrote:
> 
> Jay,
> I have seen this a few times but usually with a generator that is not
> designed for hard wired system.  I have a Ryobi
> work generator that does this on both of my outback systems.  It says
> in the instructions that it is not to be used for stationary
> applications (ie normally grounded systems).
> 
> John
> 
>> On Tue, Jan 3, 2023 at 9:16 AM Jay via RE-wrenches
>> <[email protected]> wrote:
>> 
>> Has anyone had a vfx sort of not pay attention to it charging current 
>> settings,
>> 
>> I have a customer who’s older vfx will do the following
>> 
>> Settings are 5 amps ac, 5 amp ac  charge
>> 
>> It’ll run at about 10 amps dc charging
>> Then randomly go up to 30 amps dc then back down. Maybe 15 seconds
>> Later go up to 25 amps and back down. Kinda all over the place
>> 
>> Then will stay at the lower amps for some period of time.
>> 
>> I’m thinking it’s a hardware problem?
>> 
>> And given the age a new board set is probably in order.
>> 
>> Thoughts?
>> 
>> Thx
>> Jay
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to