Hi Esteemed Wrenchies,

Love this discussion.

It is clear to me after many years of watching this that the industry needs to have an Emergency Shutdown standard that includes an emergency shutdown of the BMS of every battery as well as the inverter's circuits including MPPTs if all all-in-one.

We are pushing now for all battery and inverter manufacturers to include this feature in their inverter communications so that if the inverter emergency shutdown pins are shorted -every battery shuts down.

This would avoid the ridiculous requirement of every battery cable being on a relay/contactor or bringing it to the outside of the house!



Jerry Shafer via RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
January 30, 2023 at 5:08 PM
Wrenches.
You might want to consider turning off the inverter as a solution to turning off the batteries, we have this feature as part of our installs with outback real simple then no chance of AC anywhere, Not going to pop a CC, no chance of run on and it has passed every time. Just a thought that's a safe solution. With Outback you just have to turn off the master nothing else.
"Fun time in a crazy world"



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Brian Mehalic via RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
January 30, 2023 at 10:54 AM
Hey folks - love the Code, hate it, don’t care about it or follow it: it doesn’t matter to me. But if you want to change it you have to realize it is a process with rules and procedures, and posting on this list that “the NEC” should immediately “issue a memo” to do what you want or change what you don’t like has ZERO effect.

Brian

On Jan 30, 2023, at 4:47 AM, Christopher Warfel via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:



I don't think the discussion has forked at all.  A solution to this problem, and it is the best solution all things considered, including firefighter exposure to 10 ft of conductors that I have a hard time imaging them being exposed to,  is for the NEC to issue a memo IMMEDIATELY indicating that this section of the code is no longer to be considered a requirement and that the next Code cycle will eliminate this requirement.

The other solutions discussed would only work for a few configurations realistically and would introduce more danger. Chris



On 1/29/2023 2:41 PM, William Miller via RE-wrenches wrote:

James, Brian and others:

Thank you all for the lively discussion.  I am always interested in my colleague’s perspectives and this has been illuminating.

It appears to me the discussion has forked:  One topic is how to deal with the reality of the new code regarding a very narrow scenario: ESS inside of a residence.  The other topic is: has the NEC evolved to be overly restrictive without factual basis?

Regarding the first topic, it’s in black and white that we must provide battery disconnecting means for energy storage systems located in one or two family homes if the battery voltage exceeds 60 VDC.  There are very few areas that do not adopt the NEC.  If you install ESS you will eventually have to deal with this code requirement one way or another.

Due to lax enforcement or unfamiliarity on the part of local building departments, some of you may be able to skirt this requirement.  This is great until something happens.  If your non-compliant installation causes a loss, you will end up in the defendants chair, not the building inspector.

Here is how I approach these compliance conundrums:  If I could argue the code does not apply or there is a good reason to waive the requirement; if the building official agrees; if I feel the installation is really and truly safe without meeting the  requirement—only then could I proceed without the disconnect.  Otherwise I am going to have to find a way to comply.

As contractors, each of you makes those decisions every day: What is safe enough for my clients?  If any of you think you know more than the people who write the codes, then install what you can get away with and keep your fingers crossed.  I am not willing to live like that.

Regarding the second topic: Are we being picked on by an overly scare-mongering NFPA?

What is interesting here is that while most electrical codes are trying to prevent house fires, this particular section is trying to protect fire fighters after a fire starts (or an earthquake happens or a dump truck runs into your house, etc.).

When California first adopted roof clearances for fire fighters, I got my feelings hurt because I was losing business and I did not understand what it takes to fight a house fire.  I spoke with a few fire fighters and learned about roof and wall venting and how it is affected by prevailing winds.  I came around to appreciate there is a real need for rooftop fire setbacks.

It is self-evident why firefighters would not want to cut into a wall with a demo saw if there are energized, high amperage conductors in or on that wall.  This code requirement for battery disconnecting means is fundamentally sensible.  That ends the discussion for me.

Oh, yeah, the charge controller blowing up thing:  Does anyone have any factual data to share on this?  Regardless of that, does it really matter if the charge controller is saved but the house burns down?

The islanding thing:  To be compliant, all ungrounded battery conductors need to be disconnected.  This includes the charge controller circuit(s).  With the charge controllers and inverters disconnected from the batteries and from each other there cannot be DC “islanding”.

The house flooding thing:  At the surface, it appears you have a choice of disasters:  flood or fire.  I submit that fire is more destructive (I don’t think many people have died from a ruptured water pipe).  I don’t think it has to be either or:  Find a way to provide emergency power to freeze protection devices with that disconnect waived or under key in cooperation with the fire department.  This may mean the batteries need to remain connected.  Put those leads in metal raceway and mark their locations from the outside. Work with building and fire officials.  Limit your liability.

Thanks again to all of you for the discussion.  I know what I need to do.

William Miller

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com <http://www.millersolar.com/>

CA Lic. 773985

*From:*James Jarvis [mailto:j...@aprsworld.com]
*Sent:* Saturday, January 28, 2023 7:03 PM
*To:* Brian Mehalic
*Cc:* RE-wrenches; will...@millersolar.com
*Subject:* Re: [RE-wrenches] Remote battery disconnects

Brian and William,

With all due respect, I think your geographical location of California may be limiting in your understanding of the implications of local power security.

Where I am in Minnesota and where I work in Alaska, loss of power and backup power can have very expensive consequences. When it is -30F outside and howling wind, buildings only have a matter of hours before their interiors will drop below freezing. A few hours after that pipes start to freeze and break. Pressurized water then starts to spray everywhere and then things can very quickly run into six-figure dollars amounts of damage. So one way of reducing this risk is by installing an ESS.

Around here, prior to the latest NEC, we didn't have exterior disconnects available for anyone to shut off power. We still don't for businesses.

My point is that NEC is mandating that there be zero security of a buildings electrical systems by requiring publicly accessible disconnects on backup systems. And if NEC wasn't so prescriptive, there could be slightly more secure alternatives such as a KNOXBOX or access controlled disconnects.

William: I also disagree with your premise that you'll test the battery disconnect system after dark. That's not a test; that's just cheating. You had a knowledge person tell you that the MPPT controllers can and do blow up when they lose their voltage reference (battery) under load. And removing the battery from the circuit does allow the charge controllers to island with the inverter and DC loads and do other damage. I know of a telecom customer that had hundreds of thousands of dollars of damage when their battery became disconnected. If you are unwilling to test it at full load, I'd guess you know that the whole concept is a dumb idea.


-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727

http://www.aprsworld.com/

On Sat, Jan 28, 2023 at 7:35 PM Brian Mehalic <br...@solarenergy.org> wrote:

    Every single house I’ve looked at in my town has a breaker panel
    with a main service disconnect on the outside of the house
    already. So in many cases we are well beyond worrying about
    someone “flicking your switch!”

    In fact, in addition to the emergency disconnect requirement for
    stationary standby batteries [480.7(B)] and ESS [706.15(B)] in
    one- and two-family dwellings, also added in 2020 was the
    requirement for an emergency disconnect for services on those
    same one- and two-family dwellings [230.85].

    Brian Mehalic



    On Jan 28, 2023, at 5:58 PM, James Jarvis via RE-wrenches
    <re-wrenches@lists.re-wrenches.org> wrote:

        

        It would be nice if the decision was up to the owner /
        occupant of the property. I, for one, do not want any random
        person to be able to turn off my house or business with the
        flick of a switch. I feel strongly that there is far too
        much fear mongering in NEC with relation to renewable energy.


        -James Jefferson Jarvis
        APRS World, LLC
        +1-507-454-2727

        http://www.aprsworld.com/

        On Sat, Jan 28, 2023 at 6:22 PM William Miller via
        RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

            Esteemed wrenches:

            Well if my house is on fire and the entry of fire
            responders is delayed for lack of a disconnect, I choose
            having the disconnect. I can worry about the charge
            controllers later.

            Others may prioritize their charge controller over their
            homes…

            Put a cable-tie lock in the closed position to
            discourage kids from messing with it. Test it only after
            dark.

            William

            On Sat, Jan 28, 2023 at 2:32 PM William Bryce
            <wlbr...@pineridgeproducts.com> wrote:

                All

                One thing that no one is talking about is what
                happens to the MPPT charge controllers when the
                Battery Disconnect trips when the charge controllers
                are under full load.

                Many will blow up. Try turning off the battery
                breaker on a SolaArk  when the charge controllers
                are maxed, and see if you get lucky.

                On Sat, Jan 28, 2023 at 3:27 PM William Miller via
                RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

                    Jeremy:

                    Thanks for posting the code references for those
                    that had never looked them up.

                    Chris:

                    What do you mean by “a disconnect for AC wiring,
                    not specific to which or both panel types”?

                    All:

                    Code references are handy when receiving edicts
                    from building officials, but not required, IMHO,
                    for two reasons:  The contractor should already
                    be versed in the codes and, building departments
                    can mandate their own requirements above and
                    beyond the code.

                    It may seem redundant to require an AC
                    disconnect for premise wiring as well as a DC
                    battery disconnect.  In most cases if you
                    disconnect the inverter from the batteries the
                    AC power goes off.  However if the generator is
                    running at the time, some battery inverters can
                    operate when disconnected from batteries.  So to
                    completely de-energize all components of an
                    off-grid home you need to disconnect the
                    generator and the battery leads.

                    In this case the home is required to have fire
                    sprinklers.  There is pressure pump to provide
                    flow to these fire sprinklers-- said pump being
                    powered by the inverter/battery system.  I am
                    going to apply for a waiver to remove the DC
                    disconnect requirement on the grounds that the
                    pressure pump is essential fire suppression
                    equipment. Instead I will propose to supply an
                    AC disconnect (meeting all requirements for
                    accessibility and marking) that will disconnect
                    all premise wiring except the pressure pump.

                    By the way, I will of course be trying to apply
                    the logic that the voltage specification is for
                    nominal battery voltage and this project having
                    a nominal 48 volt bank does not require the
                    battery disconnect.

                    I will let the group know what response I
                    receive. Regardless of how this works in this
                    jurisdiction, I think these are both valid
                    arguments worth trying in any jurisdiction
                    requiring the battery disconnect. Some officials
                    are amenable to dialog and negotiation and some
                    are less so.

                    William Miller

                    Miller Solar

                    17395 Oak Road, Atascadero, CA 93422

                    805-438-5600

                    www.millersolar.com <http://www.millersolar.com/>

                    CA Lic. 773985

                    *From:*RE-wrenches
                    [mailto:re-wrenches-boun...@lists.re-wrenches.org]
                    *On Behalf Of *Jeremy Rodriguez via RE-wrenches
                    *Sent:* Saturday, January 28, 2023 10:12 AM
                    *To:* cwar...@entech-engineering.com; RE-wrenches
                    *Cc:* Jeremy Rodriguez
                    *Subject:* Re: [RE-wrenches] Remote battery
                    disconnects

                    

                    *2020 Code Language:*

                    /*480.7 DC Disconnect Methods.*/

                    /*(A) Disconnecting Means.*/*//*/A disconnecting
                    means shall be provided for all ungrounded
                    conductors derived from a stationary battery
                    system with a voltage over 60 volts dc. A
                    disconnecting means shall be readily accessible
                    and located within sight of the battery system./

                    /*N*/*//(B) Emergency Disconnect./ /*/For
                    one-family and two-family dwellings, a
                    disconnecting means or its remote control for a
                    stationary battery system shall be located at a
                    readily accessible location outside the building
                    for emergency use. The disconnect shall be
                    labeled “EMERGENCY DISCONNECT”./

                    */N/(C) Disconnection of Series Battery
                    Circuits./ /*/Battery circuits exceeding 240
                    volts dc nominal between conductors or to ground
                    and subject to field servicing shall have
                    provisions to disconnect the series-connected
                    strings into segments not exceeding 240 volts dc
                    nominal for maintenance by qualified persons.
                    Non-load-break bolted or plug-in disconnects
                    shall be permitted./

                    Jeremy Rodriguez

                    Solar Installation / Design

                    All Solar, Inc.

                    1453 M St.

                    Penrose Colorado 81240

                    Sent by Jeremy's iPhone. Sorry for typos and
                    shorthand.

                    On Jan 28, 2023, at 7:28 AM, Christopher Warfel
                    via RE-wrenches
                    <re-wrenches@lists.re-wrenches.org> wrote:

                        

                        Seems confusing that the AHJ is requiring a
                        disconnect for AC wiring, not specific to
                        which or both panel types, and then a dc
                        disconnect with no code reference.  Was
                        trying to convey a reasonable, safe
                        approach.  A lot of bad information from
                        fire department solar consultants making a
                        lot of money fear mongering, which has led
                        to this type of situation.  Chris

                        On 1/27/2023 3:35 PM, William Miller via
                        RE-wrenches wrote:

                            Glenn:

                            As I wrote, a DC disconnect is
                            required.  Here is an excerpt from the
                            Q&A with the building official:

                            4.Will you be requiring an external
                            disconnect to disconnect the AC output
                            of the inverter system from premise wiring?

                            Yes, as required per 230.85

                            5.Will you be requiring an external
                            disconnect to disconnect batteries from
                            the inverters?

                            Yes

                            If the DC disconnect was not required I
                            would not be wasting everyone’s time
                            with my post.  I try to be careful about
                            that, researching on my own before
                            posting and trying to make my questions
                            very clear.  I also try not to embarrass
                            myself with dumb questions, but that
                            does happen occasionally…

                            William

                            Miller Solar

                            17395 Oak Road, Atascadero, CA 93422

                            805-438-5600

                            www.millersolar.com
                            <http://www.millersolar.com/>

                            CA Lic. 773985

                            *From:*RE-wrenches
                            [mailto:re-wrenches-boun...@lists.re-wrenches.org]
                            *On Behalf Of *Glenn Burt via RE-wrenches
                            *Sent:* Friday, January 27, 2023 11:46 AM
                            *To:* William Miller via RE-wrenches
                            *Cc:* Glenn Burt
                            *Subject:* Re: [RE-wrenches] Remote
                            battery disconnects

                            Does the AHJ really want the batteries
                            disconnected from conductors, or does he
                            really just want the inverters to stop
                            operating and producing AC within the house?

                            Obviously there is a big difference here
                            and it may be changing as the code evolves.

                            -Glenn

                            Sent from my 'smart'phone, so please
                            excuse typos and spelling errors.

                            ------ Original message------

                            *From: *William Miller via RE-wrenches

                            *Date: *Fri, Jan 27, 2023 2:26 PM

                            *To: *RE-wrenches;

                            *Cc: *William Miller;

                            *Subject:*[RE-wrenches] Remote battery
                            disconnects

                            Friends:

                            We have a large-ish residential off-grid
                            system install coming up. The AHJ has
                            said they will require a remote battery
                            disconnect.  I suspect there will be
                            fire sprinkler controls and a pressure
                            pump that would become inoperable if
                            this system were engaged. In this case
                            we will apply for a waiver.

                            The last time this was discussed here as
                            far as I can find was October of 2020. 
                            At that time no one suggested any
                            specific battery disconnect equipment.

                            To further clarify my needs:  There will
                            be 4 or 5 Radian 8048 inverters (5 or 6
                            4/0 battery circuits, ~350A each) and
                            two 175 amp PV recombiner outputs.  That
                            is 6 poles of high amperage DC disconnects.

                            The battery array will be either a
                            UnigyII VRLA or a lithium of a brand yet
                            to be determined. In the case of lithium
                            we will look for a system that can
                            remotely enable a BMS shutdown.  In the
                            case of a VRLA lead-acid, we will not
                            have that luxury.

                            I have done some considerable research
                            and have not found viable, high
                            amperage, remotely activated shutdown
                            equipment.

                            I am wondering what hardware others may
                            be using to achieve remote battery
                            disconnecting in these types of cases..

                            William

                            Miller Solar

                            17395 Oak Road, Atascadero, CA 93422

                            805-438-5600 <tel:805-438-5600>

                            www.millersolar.com
                            <http://www.millersolar.com/>

                            CA Lic. 773985

                    _______________________________________________
                    List sponsored by Redwood Alliance

                    Pay optional member dues here:
                    http://re-wrenches.org

                    List Address: RE-wrenches@lists.re-wrenches.org

                    Change listserver email address & settings:
                    
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

                    There are two list archives for searching. When
                    one doesn't work, try the other:
                    
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
                    
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

                    List rules & etiquette:
                    http://www.re-wrenches.org/etiquette.htm

                    Check out or update participant bios:
                    http://www.members.re-wrenches.org

--

            William Miller
            Miller Solar.com
            895-438-5600
            www.millersolar.com <http://www.millersolar.com>

            _______________________________________________
            List sponsored by Redwood Alliance

            Pay optional member dues here: http://re-wrenches.org

            List Address: RE-wrenches@lists.re-wrenches.org

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            There are two list archives for searching. When one
            doesn't work, try the other:
            https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            http://www.re-wrenches.org/etiquette.htm

            Check out or update participant bios:
            http://www.members.re-wrenches.org

        _______________________________________________
        List sponsored by Redwood Alliance

        Pay optional member dues here: http://re-wrenches.org

        List Address: RE-wrenches@lists.re-wrenches.org

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        There are two list archives for searching. When one doesn't
        work, try the other:
        https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        http://www.re-wrenches.org/etiquette.htm

        Check out or update participant bios:
        http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org





_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Christopher Warfel via RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
January 30, 2023 at 6:46 AM

I don't think the discussion has forked at all.  A solution to this problem, and it is the best solution all things considered, including firefighter exposure to 10 ft of conductors that I have a hard time imaging them being exposed to,  is for the NEC to issue a memo IMMEDIATELY indicating that this section of the code is no longer to be considered a requirement and that the next Code cycle will eliminate this requirement.

The other solutions discussed would only work for a few configurations realistically and would introduce more danger. Chris



On 1/29/2023 2:41 PM, William Miller via RE-wrenches wrote:


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to