I would suggest that adding additional batteries to increase battery voltages 
is fine 48 to 54V or what ever, I too have used this many times on very remote 
sites. Please also increase your inverters hi voltage cut out settings, as this 
can be a real bummer having the system shut down in full sun. 
Another thing; IF you have battery strings,  cables of equal length from each 
string should be connected to a buss bar then buss bar to inverter or 
inverters, this will reduce wiring headaches, voltage drop as well as providing 
equal charging to all strings. (depending on internal resistance).
I would also suggest fewer batteries of bigger cells. My preference is 2 volt 
cells, less holes to water, less copper interconnects. Yeah there heavy but for 
hi charging & discharging, a large battery is always my choice.  OR the 
Surrette 6CS25P has been the MOST reliable battery Surrette has put out. After 
almost 30 + years of installing their batteries this one has been the best. 
They do have a EX series 2 Volt cell that has the same plate thickness as the 6 
CS but I have had issues w/ them. IF you are using the EX 2 volt check the 
polarity PRIOR to installing them & mark the positive side. I have had the 
plastic covers installed incorrectly and it plays havoc on your install.
Yep LEADITE I am, refractometer and a DVOM and I have a client that can spot 
problems way before things become critical. AND that Surrette warrantee Pit 
BULL Mr. Higgins & your client will be very happy when Steve OKs a replacement 
because you have recorded your Spg readings.
My $.02 TUMP
  
> On Apr 5, 2023, at 5:26 PM, greg egan via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
> 
> Danny, My experience is if you are careful and use equal length conductors 
> for all 3 strings you can get good results.  The main problem I have with 3 
> strings of 6 V cells @ 48 vdc is leaving the customer with 72 cells to check 
> and fill.  That's a lot of work if you don't have a watering system.  
> 
> I totally get why you'd want to give them 2 strings in case they lose a 
> battery or 2.  Most of my off grid customers live quite a ways from the 
> battery store and it's not uncommon for it to take a     month to get 
> replacements - during the best of times.  
> 
> Another option I've done is give them a string of 25 - 2V cells for a 48V 
> system.   You just set the charging parameters accordingly and go.  That way 
> if they lose a cell or two, the remaining battery bank should be able to keep 
> them limping along until the replacement battery(s) show up.  Need to check 
> and make sure your charge controller and inverter can charge at the slightly 
> higher V but usually that's not a problem.  
> 
> Best,
> 
> Greg Egan
> Remote Power Inc.
> 
> [email protected] <mailto:[email protected]>
> 
> 
> 
> Message: 1
> Date: Tue, 4 Apr 2023 20:45:44 +0000
> From: Daniel Young <[email protected]> <mailto:[email protected]>
> To: "[email protected]" <mailto:[email protected]> 
> <[email protected]> <mailto:[email protected]>, RE-wrenches
>       <[email protected]> 
> <mailto:[email protected]>
> Subject: Re: [RE-wrenches] replace part of rolls battery bank
> Message-ID:
>       
> <bl1pr12mb5921cde5991f65fa842bc82cbb...@bl1pr12mb5921.namprd12.prod.outlook.com>
>  
> <mailto:bl1pr12mb5921cde5991f65fa842bc82cbb...@bl1pr12mb5921.namprd12.prod.outlook.com>
>       
> Content-Type: text/plain; charset="utf-8"
> 
> Thanks all for the advice. I figured it was not worth trying on a different 
> battery brand. I honestly needed to be able to tell them I researched it and 
> asked my peers.
> 
> The client really uses the 3 x strings they have and did not really want to 
> go down to 3. They are currently choosing to get the two Rolls under the 
> prorated warranty, and hopes to get another 2 useful years out of the bank 
> before planning to replace.
> 
> Already prepared him on the cost of the equivalent Li+ at todays prices. So 
> he knows roughly where he is heading.
> 
> Side note: I am in the camp of trying for 2 x strings when possible (agree 
> that 3 x strings is the absolute limit, and not the best option), simply 
> because if a single cell goes bad, I don?t want a client with essentially 
> nothing available until we can get a replacement and get on site. With 2 
> strings, they can make due at least. That?ll go out the window with Lithium 
> though. Looking at Fortress Power for the next battery bank for this client. 
> But we will see what changes in the market by the time it?s needed.
> 
> With Regards,
> --
> 
> Danny Young
> NABCEP PV Installation Professional #031508-90
> Engineering Team Lead
> Solar Energy Solutions
> Lexington | Louisville | Bloomington | Cincinnati | Evansville | Indianapolis
> 513-448-5176 (mobile)
> 877-312-7456 (Main Office)
> [email protected] <mailto:[email protected]><mailto:[email protected]> 
> <mailto:[email protected]>_______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 






"We must all learn to live together as brothers,
 or we all will perish as fools."
MLK







> Tump 
> <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>[email protected]
>        www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to