I think the power factor will be very close to one for split phase.  What's the inverter specs say w/r to this? Chris

On 4/27/2023 5:10 PM, August Goers via RE-wrenches wrote:
Hi Wrenches,

We have a residential site with grid tied solar where there is an electrician involved who has gotten into taking site readings and thinks there is a power factor problem. My gut on it is that there is some sort of measurement reading error, and that the power factor should be around 1.

The electrician is using a Fluke 3540FC power monitor and has provided a spreadsheet comparing active power to apparent power and calculating power factor. See below (you might have to open the image and zoom in to read it). This measurement was taken with a PV system running, presumably sending some power back to the grid.  Note that the phase B active power measurement is negative (PV exporting to grid) and that the apparent power is positive. This nets in a power factor that is crazy low of 0.05.

Does anyone have experience about whether a meter like this can properly measure these readings - maybe there is a setting error or it can't deal with negative readings?

image.png

Best,

August
Luminalt

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>

BEGIN:VCARD
VERSION:4.0
N:Warfel;Christopher;;;
TEL;VALUE=TEXT:401-447-5773 (c)
NOTE:Use the cell phone number for all communications.  Thank you.
URL:https://www.entech-engineering.com
END:VCARD
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to