Darryl:


Here are a few suggestions:



1.   Don’t move to California.  Those rates are unheard of here for many
years.

2.      Grid-zero.  From the manual:  In *GridZero *mode, the Radian
inverter remains grid-connected, but prioritizes the use of battery or
renewable sources to run loads.

3.   Mini-grid. From the manual: In Mini Grid mode, the Radian inverter
automatically rejects an AC source and runs solely from battery (and
renewable) energy. The inverter only connects to the AC source (usually the
utility grid) when the batteries run too low.  While connected to the
utility grid, the inverter’s charger can be set either On or Off.

4.   HBX mode.  From the manual:  In High Battery Transfer (HBX) mode, the
system is connected to an AC source such as the utility grid; however, it
will use battery power as the fi rst priority. The AC source is locked out
until needed.

5.   Grid use time:  From the manual:  This function allows the system to
connect to (use) the utility grid and disconnect from (drop) it on a
schedule.

6.   Grid-tie:  Sell back and reduce the energy bill.



I will leave it to you to delve into these options and see if the work for
your application.  Some functions can be mixed, some cannot.



I hope this helps.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:[email protected]] *On
Behalf Of *Darryl Thayer via RE-wrenches
*Sent:* Tuesday, May 2, 2023 11:05 AM
*To:* newrewrenches
*Cc:* Darryl Thayer
*Subject:* [RE-wrenches] problem using Radian on TOU metering



Hello, I apologize for perhaps a dumb question.  I did go online to
ask Outback twice, no answer.    System Radian 8 kW and Mate3 with 2 each
1.5 kW solar arrays into 2 ea. MX60s.  Battery 20 kWh LiFe open loop.  The
owner wants the lowest energy bill.  The rates are; off-peak at 0.04/kWh
and on-peak at 0.21/kWh.  My choice is battery and solar on-peak 9:00 am to
9:00 pm.  However, the homeowner will deplete the battery on cloudy days,
AND the Outback will turn off leaving them without power.  Is there a way
to switch to grid power for this period?   I do not want to charge the
battery at this time.
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to