If you read the section carefully, it reads on both sides of "a" horizontal
ridge. It does not read "each" or "all'" horizontal ridges. I know that
this interpretation has worked in some jurisdictions in Florida. On many
hip roofs, there could be several horizontal ridges. It could be
interpreted or rationalized that the intent is both sides of the *highest*
horizontal ridge.

Unfortunately, it's rare for an AHJ around here to enforce fire setbacks at
all, so most contractors go right up to the ridge without a second thought.
I've seen my share of panels over the ridge even. The Florida Building Code
in effect now requires AHJs to enforce setbacks as they are included in the
code, but most of them never get on the roof and they do inspections by
having the contractor sign away their first born via affidavit saying that
we did what is required. Commercial work is different. Usually, the fire
marshall is involved in these plan reviews and inspections.

Long story short, we thought it was going to be a nightmare here, but as we
got to know each jurisdiction's wants, we just complied and it all worked
out. It helps to have a menu of different panel lengths to fit multiple
rows when it's a close call.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956


On Wed, Jun 7, 2023 at 3:02 PM rick--- via RE-wrenches <
[email protected]> wrote:

> Wrenches,
>
> Looking for some guidance on setbacks at ridge for PV systems. The 2018
> code states the following:
>
> R324.6.2 Setback at ridge.
>
> For photovoltaic arrays occupying not more than 33 percent of the plan
> view total roof area, not less than an 18-inch (457 mm) clear setback is
> required on both sides of a horizontal ridge. For photovoltaic arrays
> occupying more than 33 percent of the plan view total roof area, not less
> than a 36-inch (914 mm) clear setback is required on both sides of a
> horizontal ridge.
>
> In reading this
> <https://ipsunsolar.com/new-fire-code-setbacks-in-virginia-will-limit-the-size-of-solar-projects/>article
> put out by Ipsun Solar regarding the setbacks, they state that if there’s
> no PV on the opposite side of the roof no setback is required, although
> their diagram shows a 12” setback. I don’t see any exceptions in the code
> that indicate that. What’re you all doing for ridge setbacks?
>
> Thanks,
>
>
> rick brown
> SolShine Energy Alternatives, LLC
> Electrical & Solar Contracting Services
> www.SolShineEnergy.com
> Roanoke, VA
> Office: 540.235.3095
> Mobile: 540.808.9502
>
> VA Class A Contractor Lic# 2705147660
> VA Master Electrician Lic# 2710062762
> VA Alternative Energy Systems Installer
> NABCEP Certified PV Installation Professional 110112-21
>
> [image: solshine-01-18-17 copy.jpg]
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to