Dave,
Interested to hear how you all are complying with NYSERDA on bonding in the
3' perimeter outside of the array. Their QA team just points me towards the
Illsco SGB-4 lugs, but sometimes there is no graceful way for us to install
them. If we can't get easy access under a ridge cap to hide/protect the
lugs, then the only other solution seems to be Michael's idea of running
lugs/bare copper on the seams outside of the array perimeter (which
sometimes includes whole other adjacent roof sections). Aside from being
aesthetically unpleasant, I'm also skeptical that ice and snow won't grab
onto the copper and tear the lugs off eventually...
Adam

Adam Katzman (he/him)
Autonomous Energies | Owner/Operator
www.AutonomousEnergies.com <http://www.autonomousenergies.com>
(518) 567-1468




On Thu, Jun 8, 2023 at 2:33 PM Dave Tedeyan via RE-wrenches <
[email protected]> wrote:

> Also being in NYS, I have been familiar with this requirement for a long
> time. I believe the idea is that just like how any metal part in a system
> needs to be grounded, metal roof panels under solar panels are kind of part
> of the system. What if a wire comes loose and touches the roof? You would
> not want someone going up there to get zapped. I see the point that the
> worst you can do with RSD is 80V. But in NY at least, you cant really argue
> with NYSERDA if they decide they want this. I have never come across a
> building or electrical inspector here that would care about this, but
> NYSERDA does and that is where the incentive money comes from...
>
>
>
> On Tue, Jun 6, 2023 at 2:34 PM Jay via RE-wrenches <
> [email protected]> wrote:
>
>> But isn’t the whole concept of RS to prevent the energizing of say a
>> metal roof?
>>
>> The inverter sees a ground fault or ark fault. Trips off line, the RS
>> activate and now it’s less than 80v. Isn’t that what it’s supposed to do?
>>
>> What is the purpose of grounding the metal roof?
>>
>> Jay
>>
>> On Jun 6, 2023, at 10:09 AM, Glenn Burt via RE-wrenches <
>> [email protected]> wrote:
>>
>> 
>> If I am not mistaken, this derives from some UL testing that showed that
>> a metal roof may become energized during a thermal event.
>>
>> I suppose no less important than our RSD requirements...
>>
>> -Glenn
>> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>>
>> ------ Original message------
>> *From: *Jason Szumlanski via RE-wrenches
>> *Date: *Tue, Jun 6, 2023 10:25 AM
>> *To: *[email protected];RE-wrenches;
>> *Cc: *Jason Szumlanski;
>> *Subject:*Re: [RE-wrenches] Bonding Metal Roofs Part II
>>
>> I'm watching this thread with interest. Is anyone aware of any serious
>> injury or property damage caused by an energized metal roof, and if so,
>> what were the circumstances? Is bonding metal roofs a solution looking for
>> a problem?
>>
>> In response to the ground mount alternative, that isn't really an option
>> in many areas of Florida where the cost can be 50% higher or more to ground
>> mount if it's even practical due to flood level. Tile and shingle roofs in
>> Southwest Florida are being switched to metal at shocking rates in the wake
>> of Hurricane Ian, and we love it from an installer's standpoint.
>> Fortunately, I haven't run into any bonding inspection issues for over 10
>> years here.
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>>
>>
>> On Mon, Jun 5, 2023 at 8:28 PM Dave Angelini Offgrid Solar via
>> RE-wrenches <[email protected]> wrote:
>>
>>> Hey Adam,
>>>
>>> Creative solution #1  Do not install solar on any roof if you can ground
>>> mount it.
>>>
>>> Is this He Adam or the Him Adam?
>>>
>>>
>>>
>>> *Dave Angelini Offgrid Solar
>>> "we go where powerlines don't"
>>> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
>>> e-mail  [email protected] <[email protected]>
>>> text 209 813 0060 <209%20813%200060>*
>>>
>>>
>>> On 2023-06-05 3:47 pm, AE Solar via RE-wrenches wrote:
>>>
>>> Hey all,
>>> I had started a thread about bonding to metal roofs in 2018 but can't
>>> figure out how to respond via the archive. I know some things have changed
>>> since then, so I'm circling back and starting a new thread.
>>>
>>> In NY one of our inspection agencies (NYSERDA) requires bonding of metal
>>> roof panels below the array, as well as within a 3' perimeter of the array.
>>> S-5! in combination with Ironridge is now listed to bond the roof under the
>>> array (so long as you hit every pan with an attachment) but this doesn't
>>> solve the problem of trying to bond within the 3' perimeter. For installs
>>> where we are only 18" from the ridge, this means we are required to bond
>>> the adjacent roof as well.
>>>
>>> Whenever possible we install Illsco SGB-4 lugs under the ridge cap. But
>>> more and more we're finding roofs where the ridge cap feels inaccessible,
>>> tricky, or where we simply don't want to get into roof warranty issues
>>> associated with opening up a prior contractor's work.
>>>
>>> Wondering if anyone else is coming up against this and what some
>>> possible creative solutions might be. I don't want to walk away from
>>> potential projects but...
>>>
>>> As always, thanks for any thoughts
>>> Adam
>>>
>>>
>>> Adam Katzman (he/him)
>>> Autonomous Energies | Owner/Operator
>>> www.AutonomousEnergies.com <http://www.autonomousenergies.com>
>>> (518) 567-1468
>>>
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
> [image: Logo] <https://www.sungineersolar.com/>
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com <http://www.sungineersolar.com/>
> c: (607) 279-4258
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to