The battery cables being close together, twisted too if possible, help
reduce cable inductance
which can cause voltage drop across those cables at higher currents with
120 Hz ripple.
Mainly with low frequency transformer inverter/chargers.
It's better to have them closer together than far apart, especially for
longer battery cables.
🌜boB🌛
On 6/29/2023 9:24 AM, Starlight via RE-wrenches wrote:
You may already know but… Are your DC cables bonded together and
twisted where possible to reduce magnetic fields? Higher the current
and greater the loop area, the stronger the fields are. More parallel
loops, the greater the combined flux = loud Hums.
Larry Crutcher
Starlight Solar Power Systems
On Jun 29, 2023, at 8:19 AM, Kirk Herander via RE-wrenches
<[email protected]> wrote:
All,
I am in the middle of commissioning a 480kwh BP LFP battery bank,
connected to -10- OB Radian 8kw inverter/chargers.
For the DC combiner I am using midnite 2000 amp combiner boxes,
modified to mount  class T fuses on the positive bus, for both battery
inputs and inverter outputs.
For starters, I set the master inverter at a max charge rate of 20 AC
amps, which equates to a DC charge of about 74 A. All the other
inverters are automatically set to this charge rate as well.
Turning the chargers on one by one, I started to get quite an audible
vibration from the combiner box at a combined charge of about 400 to
500 A.
So I took the cover off of the combiner, which was vibrating
noticabllly by feel. Most of the noise was from the cover not fitting
tight. But the The box itself is also vibrating by feel.
I took the combined charge up to 640A dc. This level of vibration
definitely increases with an increased charge rate. And I am surprised
because after all, we’re not talking AC here we’re talking DC. It
almost reminds me of a large AC transformer in its behavior. The
vibration did not seem to be originating at the inverters, then
resonating to the combiner.
I can dampen the vibration by adding a few things, but I’m surprised
that this is happening. All connections in the combiner are tightened
properly. Ideas?
--
*Kirk Herander / **[email protected]*
*Owner|Principal, VT Solar, LLC*
*/Celebrating our 32^st  Anniversary 1991-2023!!/*
dba Vermont Solar Engineering
802.863.1202
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org