Hi Mac and All,

If you are about to do a Supply-side tap I'd encourage you to look into the many advantages of using a Feeder Tap instead - one of which is that since it's not on the load side of the Main the equipment need not be Service Rated. (not that you might not want it to be anyway.)

Be aware that Supply Side Taps make total sense when you are doing only grid-tie as you are always backfeeding and so the current produced by the solar is always cancelling the incoming utility current.  However as soon as you add battery charging to the equation from a large or multiple parallel multi-modal inverter, then you have the very real possibility of overloading the Service Entrance Conductors.  Basically if you have a 200A residential service whose Service Entrance Conductors were based on calcs that had close to maxed out the 160 Amp continuous capacity of a 200 A service, then adding 50 Amps of battery charging to that can push if over the edge.  Once you have bi-directional flow on your supply side tap you are basically adding loads to a service that may not be able to handle it in the case of large batteries with large charging capability.

Feeder Taps on the other hand force you to do 2 things 1) they limit the bi-directional current to your Main Breaker size (200 A) and 2) they then re-protect the main load panel downstream of the tap with another Feeder Tap Breaker (or larger conductor) according to NEC2020 705.12(B) - protecting it from the sum of the 200 A potential from the utililty combined with the sell-back current potential of the grid-tie inverters. (diagram attached).  With this configuration you can safely backfeed up to 160 Amps of solar into a 200 Amp service while still have a large battery bank on that system and not worry at all about overloading during heavy battery charging.

For new construction or any large install where I need to reconfigure the Service Entrance anyway we use Feeder Taps pretty much exclusively now - for sure so for anything with batteries.  It does require having a stand-alone Main Breaker and to do away with meter-main combo panels. But the safety and flexibility of what you now have to work with in terms of AC or DC coupled inverters and battery backup - including whole home backup are far superior in my book.

And for folks already having a Main Breaker that is tappable after the Main but before any busses, the Feeder Tap approach allows you to not require shut-down of the service during reconfiguration.

Hope that helps!

Best,

Jeff

Mac Lewis via RE-wrenches <mailto:[email protected]>
July 19, 2023 at 10:01 PM
Hello Wrenches,

Is there any tap devices (piercing or other) that are UL Listed for tapping on the utility side of a main breaker for a solar interconnection?   Our AHJ won't allow anything that isn't service rated.

Thanks in advance!

--



Mac Lewis

*

"Yo solo sé que no sé nada." -Sócrates

*


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to