I've done the AC relay idea as well, on Schneider that didn't have the
easy off switching like the Outbacks. The problems are:
1) Much bigger relay, much higher current on the control side as well.
It required a relay for the relay.
2) If there's a malfunction, you are messing with the main feeders for
the home.
3) The inverters are still on with their no load draw, a pair of VFX
inverters, would be 45 to 50 watts, so you could still shut the
batteries down.
I think in your case without AGS, the trick might be to add a bypass
control switch parallel to the relay, so they can manually turn the
inverters back on.
Ray
On 7/20/2023 5:15 PM, Jay wrote:
Hi Ray
This house won’t have an AGS, manual start only.
And your comments exactly, having to wait until the next day when
hopefully there is enough sun to charge the battery is iffy.
Or they could do the inverter bypass switch.
Again I’m back to why is it a worse idea to install a relay on the AC?
Thx
Jay
As to the sol ark which I never thought about it being in a sense an
AC coupled system. IE if the inverter is off it won’t charge.
I guess you’ll have to install an external battery charger?
On Jul 20, 2023, at 5:08 PM, Ray Walters via RE-wrenches
<[email protected]> wrote:
The aux off is only if the generator doesn't start. You need to set
the gen start voltage higher. Aux off is last ditch shut down, set
for 44v for lead acid, or 47 to 49v, depending on the battery and
inverter. Hopefully DC coupled PV will raise the voltage enough to
turn the inverters back on the next day.
This is my concern on Solark installs, I just noticed that the
inverter won't pass through PV, if it hits its LVD set point.
On 7/20/2023 3:04 PM, jay via RE-wrenches wrote:
HI All,
I wanted to revisit this thread for one reason.
If you turn off the inverter at the remote on/off with the AUX
relay, then starting the generator won’t have any impact as the
inverter is off.
So someone will have to go and reset the AUX relay.
Vs
If you do a relay on the AC output, when you start the generator, it
will start charging, raising the battery volts, causing the AUX
relay to close AC output relay and you’ll have power in the house.
Am I missing something?
thanks
jay
Here is the last email I think:
Mac,
I think you've got an elegant solution to the problem. All you need
is an inexpensive relay and to program the Aux output for loadshed.
I believe shutting down the inverter with the remote on/off contacts
is actually less stressful on the inverter than opening a relay or
contactor on the load side.
Kent Osterberg
Blue Mountain Solar
On 7/11/2023 5:19 PM, Mac Lewis via RE-wrenches wrote:
Hello Wrenches,
I'm trying to solve an issue with an older Outback FX system.
It's a quad stack of Outback 3648 FX inverters and he has a
couple of Fortress eVault and an unreliable generator. The
LBCO setting can't go high enough to cut out before the eVaults
cut out so he occasionally will have to direct charge the eVault
to get things running again.I'd like to use a 12V Aux relay
logic to trip the primary inverter on/off contacts before we go
into battery shutdown so the solar has a chance to recover the
system. Pretty simple overall but I wanted to see if there are
any known ill effects of doing this with substantial load on the
system. Of course, I can use a power relay but this may be better.
Thanks for your input!
--
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org