Chris, I just helped a friend with his EV (Bolt) not charging from two
stacked SW5548's...
The problem is usually those darned sharp edges created by the 3
modified square-wave inverters in series.
I guess technology is going backwards for this kind of stuff ? New
electronics designers I guess 😁
The edges mess with the zero crossing position of course along with all
the other edges that may confuse
the washing machine.
Assuming this is a single 120 VAC SW inverter, or stacked actually, try
this...
Get a 100 foot roll of say, 10 or 12 gauge wire and strip the ends off
for connection.
You CAN pull off the wire and wind it all into a coil but this using a
roll makes it easy to
start with.
Disconnect L1 (hot) from the SW output and insert the coil of wire in
between the L1 SW output
and L1 wire end.
Then connect one terminal of a capacitor from the coil/L1 wire end.
Connect the 2nd capacitor terminal to the SW5548 Neutral connector along
with the regularly
connected Neutral wire together.
The capacitor must be a AC capacitor like a motor run cap
(non-polarized) with a voltage rating,
usually around 300 or 305 VAC or higher V.
That capacitor appears in parallel with the load or washing machine in
this case.
If you can't find 100 uF (microfarad) cap, then something lower might
work like, 10 uF or 47 uF.
Realize that the voltage appearing across the output of this
coil/capacitor combination will drop
slightly. The 240 VAC version dropped about 6 to 8 VAC which was OK.
You can, if needed, use less wire or smaller capacitor microfarads to
increase the voltage but this will
also increase the ripples.
The reason I used an air coil of wire was so that no iron/steel core
would saturate when the current
starts.
Interested to know, if you try this if it works to help filter those
edges and get the washing machine to work better.
🌜boB🌛
On 9/8/2023 11:58 AM, Chris Daum via RE-wrenches wrote:
Hi folks:
I have a fellow with a Trace SW5548, purchased from us in 2001.It’s
been workinggreat for him all this time, but the dilemma is he’s
gotten a new Hotpoint washing machine, and its electronics don’t like
the old inverter.Is there some sort of power conditioner or ‘line
tamer’ available that will work for this appliance’s operation?Any
ideas would be greatly appreciated.He’s rather loathe to replace his
inverter if he doesn’t need to.
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com/>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org