Hi Bill

Looks good to me!

I like the idea of all the copper/connections behind a plexiglass dead front. 
Makes a lot of sense and seems safe. 
I’m wondering what your inspectors say about it or how you convince them?  

It’s definitely got me thinking about doing a job I have in mind with buss bars 
and plexi dead front vs 4/0 cable. 

Jay

> On Sep 21, 2023, at 9:25 PM, frenergy via RE-wrenches 
> <[email protected]> wrote:
> 
> Jay,
> 
>             I sent a diagram of my proposed arrangement and bus sizes to 
> SimpliPhi prior to installation, which they approved. The buses (copper 
> 11000) running across the terminals are 1 1/2" X 3/16", they have a rating of 
> 480 amps.  The "bridge" buses are 2" X 3/16" with a rating of 610 amps.  The 
> greatest possible charge-discharge on this pack will be ~327 amps which is 
> only 16 amps per battery.  Typically the max supply is 11.5 amps, loads are 
> less (1, 8048 Radian). The inverter cables are pairs ( +& -) of 4/0. Picture 
> attached.
> 
>              I'm never going to reach the 30 degree C. rise in temp with 
> these amperages. The reasoning was the amps moving to each battery is so 
> small that even though the batteries at the ends of the buses have more bus 
> to move through, they are so over-sized that there would be a negligible 
> difference in voltage, small enough for the BMS to handle.
> 
>             I guess the answer to your question is send your proposal to the 
> battery manufacturer, there are charts all over the internet for bus 
> ampacities. The final touch on the way for this installation is a full sheet 
> of plexiglass mounted on the front of the pack with multiple stand-offs.  
> BTW, the structural is #1, 4 X 6" doug fir, its a 76 Kwhr pack to 100% DOD. 
> We do a lot of car charging around here.
> 
> Bill
> 
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.(shipping)
> 5575 Genesee Rd. (USPS, UPS)
> Taylorsville, CA 95983
> 530.284.1925 Office/ 530.258.1641 Cell
> CA Lic 874049
> Solar powered since 1982
> Home of the Sunny side up
> 
> 
> -- 
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> <SimpliPhi's installed 2-19-23 (1).JPG>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to