Not getting this Kevin, AC2 has always been the generator input as it
allows wider frequency and voltage settings for drifting gensets.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-10-25 11:57 am, Kevin Pegg via RE-wrenches wrote:
Physically it is all the same. Software is way more complex. As Dave
mentioned, you have to follow the commissioning process.
AC1 will no longer accept generator input, it's grid-only now. So if
you have a genset you will need to move that to AC2. This is one of the
most irritating changes with the XWPro. Makes dual-generator configs a
lot more complex now.
Kevin
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf
Of Chad Waits via RE-wrenches
Sent: October-24-23 2:18 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Cc: Chad Waits <chadwa...@netzerosolar.net>
Subject: [RE-wrenches] XW Drop in replacement inverter
Wrenches,
We have a client that had us construct a solar trailer for them back in
2014-2015 timeframe. The Current XW6048-120/240-60 is cooked and I'm
wondering if the Schneider rep (or you savvy off grid guys) on here
could tell me if the newer XW Pro 6.8kW 120/240 is an exact drop in
replacement for a system including the the old power distribution panel
accessories.
Thanks!
Chad Waits
President - Net Zero Solar
945 W. Silverlake Rd, Tucson AZ 85713
Cell: (520) 270-4873
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org