Hello Wrenches,

Has anyone been able to get a CSW4048 inverter to work with battery type set to 
Lithium? When I try that it gives a F89 battery discharge over-current error 
within a few seconds. The battery is at 100% SoC and there was only the 
inverter idle loads present.

The CSW manual refers to document 976-0319-01-01 for specifics on Lithium. I 
have not been able to locate that document. Schneider tech support suggests try 
using custom battery setting, but it won't go lower than 56V when the battery 
specs request 55V max.

I specified the CSW4048 inverter for a Lithium installation not realizing until 
too late that the CSW doesn't actually offer closed-loop BMS integration. Using 
the Insight device it does interface to the BMS and allows the MPPT controllers 
to integrate for BMS derived SoC based charge control. Unclear if the BatLev 
gauge on the SCP will accurately display SoC values from the BMS.

Kevin

_______________________________________________