Sam,

As long as the CT leads are properly terminated, opening or closing the clamp-on CT core is nothing different that what a clamp-on ammeter is doing. Make a mistake and pull the leads out of the multimeter and you may have a high voltage arc. There are other problems with using a multimeter in this manner: 1) that the current ranges are usually fused and the fuse may not clear a high voltage arc, and 2) switching current ranges may temporarily open the circuit.

Kent Osterberg
Blue Mountain Solar


On 3/8/2024 8:29 AM, Sam Haraldson via RE-wrenches wrote:
Dear Wrenches,

I'm trying to determine whether or not it is acceptable to clamp monitoring CTs around hot conductors.  For this question please assume the CT wires are landed in their proper terminals and that proper PPE/safety protocol is employed. The monitored currents in question are residential services of 600A or less. Is there harm to the CT by clamping them around a hot conductor?

The physics of a CT from my brief research states that,/"...the secondary of a current transformer should not be disconnected from its burden while current is in the primary, as the secondary will attempt to continue driving current into an effective infinite impedance potentially generating high voltages and thus compromising operator safety." /This begs the question how I can use my DMM clamp meter w/o causing damage or is the italicized text related to very high current applications from the world of medium and high voltage equipment and not as pertinent to the residential and light commercial world I work in?

I suspect this is a no-brainer answer for the seasoned professionals on the list and I'll be most appreciative for any proof (no matter how brief) you wish to share.  Ultimately we wish to minimize the need to perform power shut downs and interrupt client service when installing load monitoring CTs to a home but only wish to do so if it is part of a safe and non equipment-harming process.

Sincerely,
Sam Haraldson

OnSite Energy <https://www.google.com/url?q=https://onsiteenergyinc.com/&source=gmail-html&ust=1677085494759000&usg=AOvVaw2NN36GoM1sjnS4RdC8Svt->
SAM HARALDSON
Field Operations Director
(406) 551-6135
1515 N. Rouse Ave Bozeman, MT 59715
Locally owned and operated since 2012
B Corporation <https://www.google.com/url?q=https://onsiteenergyinc.com/bcorp&source=gmail-html&ust=1677085494759000&usg=AOvVaw0EluC1lXtz2KlRFag-htKe>


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to