Just as a point of clarification: The Delta lightning arrestors (gray cans) are 
not surge arrestors and are not designed to protect sensitive electronics. They 
are lightning arrestors, it says so right on them. They are a spark Gap device 
and work on  Dv/DT.  The lightning arrestors do work for the designed purpose 
and are a good idea as a first line of defense. The surge arrestors like the 
MNSPD series are by definition a surge arrestor and specific break over 
voltages and should be used on all input and output connection points on a 
system. I would ever recommend removing a delta lightning arrestor, but would 
encourage installers to add a surge arrestor. The Delta lightning arrestors are 
useful to protect things like stator windings, transformers, and conductors, 
but they offer little protection for electronics like a surge arrestor is 
designed to do.
Pieter Huebner
Project Manager
Of grid Enterprises

From: RE-wrenches <[email protected]> On Behalf Of John 
Blittersdorf via RE-wrenches
Sent: Friday, April 12, 2024 8:09 AM
To: RE-wrenches <[email protected]>
Cc: John Blittersdorf <[email protected]>
Subject: Re: [RE-wrenches] midnite new inverter

Bill,
   Now that you mention it I did not have an SPD near the inverter,  I have one 
 on 1 of 2 TOP Racks, other rack with old Delta... My inverter lives on my 
workbench to allow swapping other inverters in for load testing using my whole 
house with everything connected to ancient wiring which did not include an SPD. 
 I put them on all my customers' systems and have had no issues on most of them 
and have never had to replace one. .  I have removed lots of those grey cans 
but have not taken care of my own system !!!  The Fortress eflex was not fully 
protected either.  That strike would have been the perfect test of the SPD's if 
I had them all installed. I  had a perfect real world test of
Outbacks ACA with surge protection  on two GVFX inverters that had annual 
lightning failure until I installed their surge protectors.  There have been no 
more failures since (at least 10 years)  The lightning was so severe at that  
location that the power company was constantly having issues on that power line.

John


On Fri, Apr 12, 2024 at 12:31 AM Bill Battagin via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:

John,

            Just curious if you had SPDs (like Midnites) in either system?  AC 
side, DC side

Bill

Feather River Solar Electric

Bill Battagin, owner

4291 Nelson St. (Shipping)

5575 Genesee Rd. (USPS, UPS)

Taylorsville, CA  95983

530-284-7849, 258-1641(cell)

CA. C10 Lic # 874049

Solar Powered since 1982

Home of the Sunny Side Up
On 4/10/2024 6:01 AM, John Blittersdorf via RE-wrenches wrote:
Time will tell where the failure modes are.   I still don't like all the eggs 
in one basket. Do you have to send the units back for repair?  Had enough of 
that with Trace SW series inverters..
For off grid, I'll stick to the tried and true for now.  For Grid tie it is 
just a financial hit.  For off-grid power loss it is more important to deal 
with right away..

I am going to try a Fortress Envy at my off grid home but will keep my Outback 
field repairable VFXR wired in just in case. I had a massive lightning strike 
between my house and a guest cabin 1/4 mile away and I lost power from my 
Fortress Eflex battery at the cabin and my Outback inverter at my house.  I 
replaced the control board on my inverter ( I always keep one in reserve as it 
is usually the only board failure due to lightning)  and was back on line in 
1/2 hour and Fortress rushed me a new BMS board for the E-flex and a day later 
and a half hour swap had it back in service,  Now it is a different story with 
2 Simpliphi batteries I have from a customer that failed.  I have to ship them 
to California to have them evaluated to see if we had damaged them by misuse.  
Lots of expense and time lost.



John Blittersdorf
CV Wind Service / Off Grid Vermont
802-770-8625

On Tue, Apr 9, 2024 at 11:43 PM Scot Arey via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Wow, are we in the golden age of inverter/chargers? If it had 200-a.p pass thru 
it would be near perfect.

Begs the question: are stand alone charge controllers becoming a historical 
artifact?

Howard "Scot" Arey
Owner, Solar CenTex
254-300-1228
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________

List sponsored by Redwood Alliance



Pay optional member dues here: http://re-wrenches.org



List Address: 
[email protected]<mailto:[email protected]>



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



There are two list archives for searching. When one doesn't work, try the other:

https://www.mail-archive.com/[email protected]/

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

http://www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

http://www.members.re-wrenches.org



[https://s-install.avcdn.net/ipm/preview/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
Virus-free.www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to