Mac,
I have a system that does this (or something similar) with all of the
Insight data a few times every day. I'm pretty sure it is lost data
resulting from communications drop outs. Internet to the site is via
StarLink. If you are only seeing this on the SOC data there might be a
problem with the Xanbus connection to the battery monitor. Since the SOC
returns to the correct value for the next data packet, I'm pretty sure
that there is nothing wrong with the battery monitor.
Kent Osterberg
Blue Mountain Solar
On 5/3/2024 6:54 AM, Mac Lewis via RE-wrenches wrote:
Hello Wrenches,
I have a system that suddenly started seeing quite a few SOC drops and
blips, causing generator starts.
Here is an example SOC chart:
image.png
I plan to head up and apply a firmware update on the batteries, check
cabling etc but Im curious if anyone has encountered/solved this issue.
Much appreciated.
--
Mac Lewis
*
"Yo solo sé que no sé nada." -Sócrates
*