Michael, it is super scary to hear these stories and they are a good
reminder that Li-ion technology still has risks. I am glad the manufacturer
is taking care of you, but it is concerning to see that the battery safety
systems allowed the thermal runaway event.

Hopefully, the fire department coded the incident response correctly, so
the powers that be can understand this was a li-ion thermal event from a
home energy storage system.

As more and more ESS systems enter the market, getting a recent UL 9540
listing is important. The earlier versions of the standard were less
robust, but the current edition of 9540 requires UL 9540A testing to be
performed for indoor installations to establish minimum room size based on
25% LFL.

It looks like there will soon be a UL 9540B requirement, and the outline of
investigation is just circulating. I see one Discover datasheet shows UL
9540 listing, but I didn't do research into what edition they tested to, or
if this was the same unit that exploded.

The issue with the 9540A thermal runaway testing is it might not have
tested for this failure mode, but the conditions you describe are very
similar to what 9540B intends to test.

I know many feel LFP is a safer battery than NMC or other li-ion
chemistries, but these events show that the LFP batteries do fail, and when
they do, they can cause large sudden deflagration events without other
warning. An NMC battery pack buy contrast will usually fail by burning
until it is consumed, which might at least set off a smoke or heat
detector.

Were there any fire detection measures in the shed such as a heat or smoke
detector?


*Vince Jolissaint |* *Director of CAD Services*

2557 Wyandotte Street | Mountain View, CA  94043
Office: 650.938.9574 | Email: [email protected]






>
> Date: Mon, 27 May 2024 20:40:00 -0700
> From: Michael Morningstar <[email protected]>
> To: RE-wrenches <[email protected]>
> Subject: [RE-wrenches] Discover AES exposion
> Message-ID:
>         <
> capwhfaegnz5vjmkflffea6my+cdjqde-uuabg1_mdyuilob...@mail.gmail.com>
> Content-Type: text/plain; charset="utf-8"
>
> Hey Everybody,
>
> I wanted to circle back on the Discover AES explosion that I reported a few
> weeks ago. As far as we know, there was a thermal runaway situation. Gas
> from the battery filled the power room and then ignited causing an
> explosion. It was hot enough that anything plastic melted. The steel man
> door blew off its hinges. Beyond that, we are still trying to figure out
> why it happened.
>
> For now, what I want to say is that Discover has been awesome. The VP, CEO
> and crew responded immediately. They are paying for the cleanup of the
> building by a specialized remediation company, offered to pay to have the
> building rebuilt, 2nd day shipped new rack mount batteries and a pre-built
> Schneider system to the site. Are paying a plumbing contractor to replace
> all of the plumbing (booster pump, pressure tank and significant treatment
> equipment. Flying Mike Wight (ace off-grid installer and
> applications engineer for Discover) to the site for the rebuild. And
> reimbursing me for my involvement. This with no coercion or dawdling about.
> As soon as they found out, they were on it. I spoke with the VP and CEO and
> they genuinely care about my clients and want to do right for the sake of
> doing right, not to avoid litigation. Tell me of another RE company, or any
> company for that matter that would respond this way.
>
> --
>
> Michael Morningstar
>
>
> Morningstar Electric Inc
>
> PO Box 1494
>
> Mount Shasta, CA 96067
>
> 530-921-0560
>
> CSLB 1116835
>
> [email protected]
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to