Very interesting. Thanks for this information. It seems like Tesla has
implemented PCS in the way that I hoped it would be. They can set an
aggregate current limit from all sources feeding a bus.

Unless I am mistaken, Enphase can only limit based on a selected
ampacity of *backfeed* from their System Controller to a main panel.
It does not measure the incoming utility power and set an aggregate
output limit from all sources. That results in a 40A backfeed limit on
a 200A panel, which does not make sense to me.

I hope I have this wrong.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208

On Tue, Aug 6, 2024 at 10:30 AM August Goers <[email protected]> wrote:
>
> Hi Jason -
>
> There are many options on how a manufacturer can implement Power Control 
> Systems (PCS) and based on my experience with Tesla products, I'd say it's 
> the best thing since sliced bread. I expect that all major manufactures will 
> be implementing more advanced PCS features as soon as they are able to 
> develop and list them.
>
> But, getting back to your question - one PCS variant is a simple conductor 
> limit setting that stops controlled equipment output when a certain set 
> current limit is reached. This, as you point out, may not be the best choice 
> for large PV/inverter systems. Another PCS setting involves setting a 
> controlled "virtual panel" where all inputs are monitored. This PCS setting 
> can be, for example, 160 Amps in your 200 A meter/main example. Here is more 
> info on how that works: 
> https://service.tesla.com/docs/Public/Energy/Powerwall/Powerwall-2-Backup-Gateway-2-Installation-Manual-NA-EN/GUID-D71DFD63-1414-4915-B7A5-7E48703100DE.html
>
> I'm working on learning more about Enphase systems currently since SunPower 
> is filing for bankruptcy, so it's good to learn what Enphase can and can't do 
> at this point.
>
> Best, August
>
>
> On Thu, Aug 1, 2024 at 10:40 AM Jason Szumlanski via RE-wrenches 
> <[email protected]> wrote:
>>
>> Note: This email is written from the perspective of the Enphase
>> terminology, but the concept and question is the same in a general
>> sense.
>>
>>
>> I am having a hard time understanding the logic and benefit of a power
>> control system that is used for avoiding a main panel upgrade in a
>> typical residence. If you have a 200A main panel bus with a 200A main
>> breaker, the current limit for a backfed breaker is 32A from the PV,
>> no matter what. The PCS will artificially reduce the PV output to 32A
>> when it could be capable of a much higher current for large systems
>> depending on sunlight availability. That would waste a lot of energy
>> if the PV system is significantly larger than a 32A output rating.
>>
>> The PCS standards seem to have missed the mark. Wouldn't it make more
>> sense to limit the total current delivered to the bus from all
>> sources? For example, in the example above, if PV is delivering 40A,
>> why not allow limiting utility input to 120A for a total of 160A
>> continuous delivered to the bus before PV is throttled? If the utility
>> is delivering zero, the PV could deliver all the way up to 160A the
>> the bus if capable. That way, all of the loads would be powered to the
>> maximum extent from PV with the excess exported (if allowed via net
>> metering from the serving utility).
>>
>> Am I missing something about how PCS works? I just don't see many use
>> cases for main panel avoidance that are in customers' best interest.
>> If we can't meet the 120% rule, we just do supply-side
>> interconnections so nothing is wasted. But a backfed breaker would be
>> so much easier if PCS were implemented in the way that I would like it
>> to work.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to