Dana,

            You must have quite a bit of PV to switch out to 2 FM100's.  You didn't mention what is the size of your battery and its chemistry, what's you C-rate?  If you're charging a large Lead acid battery and maybe it was discharged pretty deep and/or you have substantial loads once you hit absorb, once its reached absorb it may continue to process pretty high amps to hold that voltage as it works on finish charging a large pack up to 100%. How long is it putting out 2800 watts per CC?

            Obviously this doesn't apply with L-ion

Bill

Feather River Solar Electric
Bill Battagin, owner
4291 Nelson St. (Shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA  95983
530-284-7849, 258-1641(cell)
CA. C10 Lic # 874049
Solar Powered since 1982
Home of the Sunny Side Up

On 9/7/2024 3:49 PM, Dana Orzel via RE-wrenches wrote:
OK, you wise guys.
I am upgrading my home off grid system from two FM 80s to two FM 100s.
The FM 80s were able to share the negative wire so you didn’t have to pull a 
second negative wire.
I wired the FM 100 typical of how my FM 80s were wired with a number four 
battery negative assuming and yes, I know what happens when I assume, that the 
PV negative on the battery negative are common and I could just pull one number 
four since going through those double 1” - 90° is a bitch. Currently I have two 
# fours for output to battery, the number eight ground and 1 # six PV input.
I got this all together and it’s charging just fine but once the battery got 
full charge controllers continued to produce full output. The battery dropped 
to a float and I had 2800W on each charge controller continuing to be produced 
at which was turning into heat so the FM 100s were getting very warm. The fans 
had not turned on, but the heat sinks were definitely very very warm to the 
touch. The battery voltage is fine.
I Read the manual it doesn’t talk about being able to use one negative so I am 
assuming that my problem is that the PV needs a negative and they do not share 
the negative.
Has anybody else seen this or done the same wiring maneuver.
  thanks in advance

Dana Orzel - [email protected] - 208.721.7003
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


--
This email has been checked for viruses by Avast antivirus software.
www.avast.com
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to