There is a large misunderstanding about lithium battery LVD voltages vs type.

Simpliphi for example has a very high LVD at between 24-25v depending on DOD 
you want.  
And thats true, the VFX/FX you can’t set the LBCO that high so you have to get 
creative. 


Vs most of the better prismatic cells, at around 20-21v LVD ( which is all I 
use)
Which every legacy inverter I know of has a higher LBCO set point than that.

Jay






> On Sep 18, 2024, at 7:22 AM, Mac Lewis via RE-wrenches 
> <[email protected]> wrote:
> 
> Hi David,
> 
> This upgrade comes up a lot.  You are at a point where you have to decide; do 
> I match my old equipment with a new 24V Lithium battery bank (thus limiting 
> my battery bank options), or do I upgrade my equipment to 48V which opens up 
> the brands available?
> 
> I have had good success matching older equipment with new batteries but my 
> preference is always to try to get these systems to 48V if it's financially 
> viable.  Ray describes a solution to get the LBCO high enough to shut off the 
> inverter before the BMS shuts down and this works.  You can also hardwire a 
> power supply to wake up the BMS directly from the generator.
> 
> Remote monitoring is very useful too, especially in a rental scenario like 
> this.  It may be time for a full upgrade.
> 
> Very hard to know which companies will make it through...
> 
> 
> 
> On Tue, Sep 17, 2024 at 4:01 PM Jason Szumlanski via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
> I don’t want to stray too far off track, but it’s worth discussing how 
> challenging it is to predict which manufacturers will be around in a few 
> years.
> 
> I know this might be a touchy subject, but Enphase is beginning to offer full 
> off-grid support. While I’m fully aware of the drawbacks of their system 
> architecture for off-grid setups, it’s also important to acknowledge that no 
> manufacturer is “too big to fail”—but Enphase is about as close as we have 
> right now. If something were to happen to them, the reliance on remote access 
> for the system functioning is concerning. It could essentially become a big 
> brick if a service issue arises and there’s no support. On the other hand, 
> Enphase may be a safe bet for certain off-grid systems if you think they will 
> come out on top. 
> 
> But the reason I bring Enphase up is modularity. Building systems with 
> interconnected components from various brands can spread the risk. Sol-Ark, 
> with its “battery agnostic” approach, is a reasonable choice, as long as 
> there’s a replacement all-in-one option if they were to go out of business. 
> EG4 and Midnite seem to offer alternatives in that space now. As long as 
> LiFePO manufacturers stick with 48V/51.2V standards, complete battery 
> replacements should be straightforward. However, I do think that large 
> battery sizes like 5 kWh (or even 13.5 and 14.3 kWh) could be problematic. 
> Personally, I prefer the concept of smaller, 1 kWh chunks. In the case of a 
> 40 kWh battery bank, for example, if one module fails and the manufacturer is 
> no longer around, it’s a lot easier to deal with. That's similar to how we 
> can drop one faulty 2V cell in a series of 24 lead acid batteries sometimes. 
> Enphase, if you think about it, is the least modular approach in some ways, 
> since it relies on a single manufacturer with a proprietary system. So the 
> whole concept of modularity is not straightforward, either. It's a fantasy at 
> this point to hope for a truly modular and manufacturer-agnostic system.
> 
> What I find interesting is that most of my clients who went off-grid 7-15 
> years ago are pretty understanding when I tell them it’s time to replace 
> their systems. Realistically, fast-forward another decade, and we’ll probably 
> see significant advances that make a complete system replacement worth it 
> once again. I’m not saying we should be designing disposable systems, but 
> that might be where we’re headed, just like so many other industries. Think 
> of what Tesla is doing with the Powewall 3. They are making solar and 
> batteries as cheap as possible (while maintaining high quality standards and 
> keeping fuel in Elon's jet). However, when the PW4 comes out, the PW3 will be 
> deprecated, and those systems will become essentially disposable. The 
> warranty is only 10 years. So when the inverter insude the PW3 dies in year 
> 11, guess what – the entire PW3, battery and all, may be rendered useless. 
> But, people still flock to Tesla for backup systems. And for good reasons. 
> 
> The days of keeping systems running on old components while upgrading just 
> parts of the system are probably behind us. The rapid evolution of 
> technology, equipment, codes, safety, and consumer needs will make whatever 
> we install today obsolete soon after it's up and running. 
> 
> 
> 
> --end rant--
> 
> 
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
> 
> 
> On Tue, Sep 17, 2024 at 5:20 PM Ray Walters via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
> Honestly, that advice would seem to  be true, but the reality is: It is 
> not valid.  Just look at Blue Planet, that was supposed to be a top tier 
> offering.  Solar World?  AEE? Magnum has had serious issues, Outback 
> doesn't answer the phone, SImpliphi takes an attorney to honor their 
> warranty. Even long standing companies are not sure bets, at all.  They 
> do cost much more, so I'm not sure who to turn to anymore.  I'm about to 
> install Rubix LiPO4, which comes in a 24 v offering, BTW for Dave.
> 
> The biggest issue I've seen with old VFX inverters, is the LVD set point 
> can't go high enough for LiPO4.  I use the aux out on a charge 
> controller, to switch on and off the remote switch on the VFX.
> 
> I like the Fortress with Solark combo, but its not without its troubles 
> either.  If the Solark shuts off due to low voltage, so does your PV 
> input.  Then the no load draw on the Fortress eventually shuts down the 
> battery.  You really need some (at least 1 kW) of DC coupled PV to keep 
> that death spiral from happening.
> 
> Ray Walters
> Remote Solar
> 
> On 9/17/2024 12:23 PM, Sindelar Solar via RE-wrenches wrote:
> > Jerry,
> > Re your advice to never get startups or small manufacturers as so many 
> > disappear and now you are stuck, I guess we should stick with the big 
> > well-established manufacturers, like Outback, Magnum and Blue Planet, 
> > right?
> > As you would say, fun times...
> > Allan
> >
> > On 9/17/2024 10:58 AM, Jerry Shafer via RE-wrenches wrote:
> >> Dave,
> >> I would suggest stepping up to 48 nominal, fortress 18.5, battery 12 
> >> or 15 k solark inverter, re-wire the array to single or dual string, 
> >> make the wiring in the home capable of 240, this usually requires 
> >> main panel re-work and set up the monitoring.
> >> Batteries are like replacement heart valves, never get startups or 
> >> small manufacturers as so many disappear and now you are stuck.
> >> Fun times.
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > Pay optional member dues here: http://re-wrenches.org 
> > <http://re-wrenches.org/>
> >
> > List Address: [email protected] 
> > <mailto:[email protected]>
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> >
> > There are two list archives for searching. When one doesn't work, try 
> > the other:
> > https://www.mail-archive.com/[email protected]/ 
> > <https://www.mail-archive.com/[email protected]/>
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> > <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> >
> > List rules & etiquette:
> > http://www.re-wrenches.org/etiquette.htm 
> > <http://www.re-wrenches.org/etiquette.htm>
> >
> > Check out or update participant bios:
> > http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> >
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> 
> 
> -- 
> 
> 
> 
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to