The enphase MPPT voltage range seems low to me.

I reviewed a few of the newer string inverters and they are between 90-200v and 
500+
A range of about 2.5 -5.5.

Enphase is around 1.8X

AP systems is about exactly the same as Enphase. 

Hoymiles a newer company that now has full range of products is 16-60v MPPT 
range on its micro, 3.75X

Always lots to consider even with a micro.

Jay



> On Sep 25, 2024, at 7:29 AM, jay <[email protected]> wrote:
> 
> Hi Vince,
> 
> Your math looks correct of course, but I think you left out a variable in 
> that the panel won’t be operating at max power because the inverters are all 
> less than 400 watts rated. 
> Which means that the MPPT voltage will be pushed up to reduce power giving 
> you added room.  
> 
> From my understanding of how the Mppt works, but I don’t know specifically 
> about enphase, if its a good algorithm the inverter won’t go below its lowest 
> MPPT voltage.  
> The inverter will reduce power playing around with the IV curve to maintain 
> the MPPT within its range.  So it won’t ever get out of operating unless it 
> can’t even produce enough volts to make that voltage.  I’ve never seen a 
> curve of Enphase MPPT efficiency vs input voltage.  Would like to though. 
> 
> 
> 
> Jay
> 
> 
> 
> 
> 
>> On Sep 24, 2024, at 8:38 PM, Vince McClellan via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> 
>> Hello Wrenches List
>> I've recently become aware of an issue with micro-inverters that I would 
>> like to share. 
>> Be sure the solar module you're using is compatible with the microinverter 
>> for the solar module's full life. 
>> A good best practice is to design for the MPPT voltage range of the 
>> inverter. I only consider the operating range of the inverter when it won't 
>> affect the inverter during its operational time, such as when the solar 
>> module is at its coldest in the first few moments of sunlight when it hits 
>> max Voc. That will only happen for a few moments as the sun heats the solar 
>> module. High heat is different. If the solar module falls below the MPPT 
>> voltage window that will happen in the middle of the day when the solar 
>> array should be producing its maximum power for the day. If the voltage of 
>> the solar module falls below the MPPT voltage window during that time it 
>> becomes much less efficient at tracking the power or simply turns off. Some 
>> studies have shown a solar module degradation rate averaging up to 
>> 1.4%/year. 
>> 
>> Here is an example of what I'm talking about with weather data for Eugene OR 
>> and a roof-mounted Phono PS400M6H-18/VHB solar module. 
>> Vmp 30.85
>> Coe/°C = -0.28%
>> High-Temperature voltage calculation: 30.85 Vmp X [ 1-(32+30-25) X .0028] = 
>> 27.65 Vmp adjusted for 2% average high temp of 32°C
>> Here is my Enphase cheat sheet for quickly looking at design compatibility.  
>> Enphase M#   Operating Range MPPT Voltage Range      Commonly used module 
>> pairings   Phase
>> IQ8MC-72-M-US        18-58 V 25-45 V 260-460 Wstc    1
>> IQ8-60-M-US  16-48 V 27-37 V 235-350 Wstc    1
>> IQ8PLUS-72-M-US      16-58 V 27-45 V 235-440 Wstc    1
>> IQ8H-3P-72-E-US      16-63 V 28.5-45 V       320-540 Wstc    3
>> IQ8M-72-US   16-58 V 30-45 V 260-460 Wstc    1
>> IQ8A-M-US    16-58 V 32-45 V 295-500 Wstc    1
>> IQ8A-72-M-US 16-58 V 32-45 V 295-500 Wstc    1
>> IQ8P-3P-72-E-US      16-63 V 35.5-53 V       380-640 Wstc    3
>> IQ8H-208-72-M-US     16-58 V 36-45 V 295-500 Wstc    1
>> IQ8X-80-M-US 25-79.5 V       43-60 V 320-540 Wstc    1
>> So I'm good with three of the inverters on my list right? Not really. As the 
>> solar cells age the degradation of the cell drops the cells voltage. A good 
>> design practice is to drop the adjusted Vmp down 10% to make up for cell 
>> degradation.  So, 27.65 Adjusted Vmp - 10% would be 24.88Vmp. I would still 
>> feel comfortable using one of the inverters on my list. 
>> If I go to the Enphase compatibility calculator 
>> <https://enphase.com/installers/microinverters/calculator> it shows seven 
>> inverters that are compatible with the Phono PS400M6H-18/VHB solar module 
>> for my climate. 
>> 
>> Other than that issue, we try to use micro inverters only when they are 
>> reasonably easy to get to because we know we will be back at some point to 
>> replace inverters. 
>> Electronic components fail mostly based on temperature fluctuations over 
>> time. The area behind a solar array is both the hottest and coldest location 
>> at the installation site. I do like micro inverters for many applications 
>> where there are multiple roof angles and or moving shade to deal with on a 
>> client's roof. 
>> 
>> I would love to hear back from others if you think my calculations are way 
>> off. This kind of back and forth is how we grow as installers and I won't 
>> take offense if any of you slam my ideas. 
>> 
>> Thanks to all of you for contributing to our industry, 
>> 
>> Vince McClellan
>> President
>> NABCEP PV Professional
>> p: 541-485-8122
>> a: 860 Conger St. Suite 12,. Eugene, OR 97402
>> e: [email protected] <mailto:[email protected]>
>> w: SolarEnergyDesign.com <http://solarenergydesign.com/>
>> CCB# 161672
>> 
>> 
>> If you have received this email and are not the intended recipient, please 
>> delete this email. Copying or using any part, content, or attachment of this 
>> email is strictly prohibited.
>> 
>> 
>> 
>> On Tue, Sep 24, 2024 at 1:55 PM Jason Szumlanski via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> It's very curious how there are geographic preferences, and that is 
>> definitely something to consider. I tell clients that there won't be anyone 
>> to service their system 10 years down the line if they go with anyone but 
>> Enphase around here. If a prospective client has 10 quotes locally, 9 of 
>> them will be Enphase, and one will be Tesla. If they get an 11th quote they 
>> might get a Franklin WH or another brand if they are doing battery backup. 
>> Even SolarEdge is dead here, as far as I can tell. I haven't seen a 
>> competitive quote with SolarEdge in ages.
>> 
>> I can share this poignant advice with clients because I'm one of the only 
>> people in Southwest Florida who will even touch something from Outback, 
>> Scheneider/Xantrex/Trace, Sonnen, Magnum, SMA, or even old grid-tied Fronius 
>> IGs. If someone wants to come and swap out HD Wave inverters as a living 
>> here, I will gladly step aside. Swimming against the current gets very 
>> tiring for consumers. Sometimes, you just have to follow the crowd.
>> 
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>> 
>> 
>> On Tue, Sep 24, 2024 at 4:41 PM August Goers <[email protected] 
>> <mailto:[email protected]>> wrote:
>> I agree with Jason that it is going to take a really compelling 
>> microinverter product at this point to knock Enphase off the #1 micro 
>> position. It seems risky to sell any other microinverter products given the 
>> complexity of the product and the fact that if the competing product 
>> manufacturer goes out of business that there won't be any choice but to 
>> replace all of that product. That said, competition in the market is good, 
>> so my salutes to anyone willing to try other microinverter products. We have 
>> experience with SolarBridge (they were owned by SunPower for a while) and 
>> that product was by far inferior to Enphase. We've also installed a few 
>> hundred PowerOne ABB micros - those have been for the most part very 
>> reliable, but the monitoring side of the equation is very poor so dealing 
>> with RMA issues there is a bit of a challenge. Both of those products are 
>> outdated now and no longer on the market.
>> 
>> I've posted here on this before - we're having good luck with the Tesla 
>> solar inverter. It is low cost and has lots of benefits including 4 x 
>> trackers with low start voltage, power control systems, built in monitoring, 
>> etc. We're now offering Enphase systems as well (we were a SunPower dealer 
>> for many years) so customers can have a choice if Tesla is not their cup of 
>> tea. Elon Musk is aggravating.
>> 
>> August
>> Luminalt
>> 
>> 
>> 
>> On Tue, Sep 24, 2024 at 1:21 PM Jason Szumlanski via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> I don't really understand the resistance to Enphase on a roof (anymore, at 
>> least). We have many thousands of microinverters out there, and I don't even 
>> have a dedicated service department. We swap maybe 100 a year at the most at 
>> this point, and that includes for systems we didn't install. It's super 
>> quick and easy. But most of our roofs are single story 5:12 pitch on average.
>> 
>> I have at least a dozen small commercial sites with 100 - 500 units each, 
>> and I can't remembereven an handful of replacements on those over the years. 
>> 
>> I did get involved with a commercial site I did not install, and that was a 
>> nightmare, with over 100 early generation microinverters that failed. It was 
>> a custom rack, and the clamps were a nightmare, not to mention the array map 
>> had gotten out of whack over the years from prior micro swaps. But for the 
>> most part, I have no issue with micro swaps on roofs. 
>> 
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>> 
>> 
>> On Tue, Sep 24, 2024 at 2:14 PM Dave Angelini Offgrid Solar via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> I am with Chris except I might put them on a barn roof ! Never a residence 
>> and never Offgrid !
>>  
>> Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>>    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ 
>> <https://offgridsolar1.com/>  <http://members.sti.net/offgridsolar/>
>> e-mail  [email protected] <mailto:[email protected]>
>> text 209 813 0060
>> 
>> 
>> On 2024-09-24 10:16 am, Chris Schaefer via RE-wrenches wrote:
>> 
>>> Was an Enphase installer since the beginning, I think 08' but moved away 
>>> when the tech support and early model failures were numerous. Moved to APS 
>>> with the two modules per micro. Really saved on install time as it was half 
>>> the number of micro's. One recommendation regardless of brand, don't put 
>>> them on a roof.
>>>  
>>> Christopher
>>> 
>>> On Tue, Sep 24, 2024 at 11:14 AM Bryan Norkunas via RE-wrenches 
>>> <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>> I've had great luck with APS and so have our local installers.
>>>  
>>> Bryan Norkunas 
>>> PV-Cables Inc.  
>>> 989 Milton Ave Ste 1D 
>>> Ferndale CA 95536 
>>> (707) 923-3000 office 
>>> www.pv-cables.com <http://www.pv-cables.com/> 
>>>  <Outlook-u2wnspqb.png>
>>>  
>>> <Outlook-kadxvmqu.png>     Please print only if necessary. 
>>>  
>>> NOTE: This email message and any attachments are for the sole use of the 
>>> intended recipient(s) and may contain confidential and/or privileged 
>>> information. Any unauthorized review, use, disclosure or distribution is 
>>> prohibited. If you are not the intended recipient, please contact the 
>>> sender by replying to this email, and destroy all copies of the original 
>>> message. 
>>>  
>>> From: RE-wrenches <[email protected] 
>>> <mailto:[email protected]>> on behalf of greg egan 
>>> via RE-wrenches <[email protected] 
>>> <mailto:[email protected]>>
>>> Sent: Monday, September 23, 2024 7:29 PM
>>> To: [email protected] 
>>> <mailto:[email protected]> 
>>> <[email protected] 
>>> <mailto:[email protected]>>
>>> Cc: greg egan <[email protected] <mailto:[email protected]>>
>>> Subject: [RE-wrenches] favortie micro inverters?
>>>  
>>> Esteemed wrenches,
>>> 
>>> Have a client that is grid connected (not my usual client) and looking 
>>> to do solar without back up.  Has shading issues so I'm thinking micros 
>>> would work best for this application, plus take care of rapid shut down 
>>> without needing extra devices/wiring.  Problem is I have not ever 
>>> installed micros.
>>> 
>>> Any recommendations on brands /models that have been reliable? Decent 
>>> tech support?  Customer just wants something that works and is 
>>> relatively simple to navigate the online monitoring.  Probably 4-5 kW so 
>>> not a huge system.
>>> 
>>> Thanks in advance, I appreciate it!
>>> 
>>> Greg Egan
>>> Remote Power Inc.
>>> Fairbanks, AK
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/ 
>>> <https://www.mail-archive.com/[email protected]/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/ 
>>> <https://www.mail-archive.com/[email protected]/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>>> 
>>>  
>>> -- 
>>> Chris Schaefer's
>>> <blocked.gif>
>>> Tel 585-229-2083 or Cell 585-748-1870 
>>> 5115 S Hill Road ~ Canandaigua New York 14424
>>> www.solarandwindfx.com <http://www.solarandwindfx.com/> ~ E-mail: 
>>> [email protected] <mailto:[email protected]>
>>> <blocked.gif>
>>> 
>>> Thomas Jefferson, the author of our great Constitution, once said, 
>>> "democracy" will cease to exist when you take away from those who are 
>>> willing to work and give to those who would not."
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/ 
>>> <https://www.mail-archive.com/[email protected]/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to