Thx Wayne.

Curious, I guess they are in a sense AC batteries, as there is no way to access 
them for DC jump charge?

And I guess that is the same with Tesla?  In that there is not way to access 
the battery, or they didn’t figure you’d actually have a true black start?

thanks for the info.

jay



> On Sep 30, 2024, at 5:51 PM, Wayne Irwin via RE-wrenches 
> <[email protected]> wrote:
> 
> Hurricane Helene has taught us the hard way that Enphase batteries with 
> anything other than IQ8's won't restart.
> The issue is that when the batteries try to restart (at the non-programmable 
> time of 9:AM) if there are any significant loads, the batteries will not stay 
> on long enough (300+ seconds) for any non-IQ8 micros to energize. The battery 
> will attempt multiple times, but if there is a load, (such as a well pump) 
> the draw from the load will essentially prohibit the batteries from 
> energizing the micros long enough to engage and produce. The only solution is 
> to have a load controller or turn off all loads once the power goes out. 
> Otherwise, during these "attempts to turn on" power in the house will 
> momentarily turn on and back off and potentially drain the batteries down to 
> lower than the point of which they can even attempt to restart. I spoke at 
> length with Enphase upper engineering (not tech support) about this today. 
> They now know that most of the tech support staff does not know this 
> important information. 
> 
> Once the batteries are dead, they are very difficult if not impossible to 
> jump start with a generator. At the recommendation of tech support we tried 
> multiple times with the "approved" inverter generator which ultimatly just 
> wasted our time. Even though the controller/switch will accept the gen power 
> and pass the energy to the loads, it will not energize the combiner or 
> batteries. If your goal is to have an autonomous system with Enphase, it's 
> only going to happen with the IQ8's (at this point).
> 
> This is a significant issue with retrofitting older systems.  
> 
> By the way:
> - We've received numerous desperate calls from (orphaned) Powerwall owners 
> whose systems also won't turn back on. 
> - ALL of our Outback systems were issue free.
> 
> I hope this helps some of you. Good Luck out there!
> 
> Wayne Irwin
> President
> License #CVC56695
> State Licensed Solar Contractor
> Pure Energy Solar International Inc.
> [email protected] <mailto:[email protected]>
> PureEnergySolar.com <http://pureenergysolar.com/>
> SolarChargingStation.com <http://solarchargingstation.com/>
> 352 377-6527 Office
> 352 336-3299 Fax
> 
> 
> The Sun Is Always Shining!
> 
> The content of this message is Pure Energy Solar Confidential. If you are not 
> the intended recipient and have received this message in error, any use or 
> distribution is prohibited. Please notify me immediately by reply e-mail and 
> delete this message from your computer system. Thank you.
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to