I have switched to Radians to get back to where we were with SW4048’s.
Also split phase and Optics make a good package.  Heavy and wiring are a
nuisance but reliability has been good and the few issues solved with board
or module swaps.  BUT with Outback in Limbo ?????


On Thu, Oct 24, 2024 at 5:14 PM Todd Cory via RE-wrenches <
[email protected]> wrote:

> One of the unfortunate changes from the SW to FX /FXR inverter
> architecture was the elimination of two AC inputs. The whole point of a
> battery based inverter is for backup power, so this becomes a huge issue
> when a grid tied system has a grid outage long enough to
> necessitate generator charging.
>
> That is why people either opt for an external Iota style charger, or the
> famous "DT Kludge", which is what I have on my home system for those rare
> times when I need generator charging.
>
> Todd
>
>
>
>
> On Thursday, October 24, 2024 4:55pm, "Bradley Bassett via RE-wrenches" <
> [email protected]> said:
>
> As I remember the FXR inverters will rarely connect to any generators
> beside very well controlled or inverter type generators. I agree that I
> don't think there is any automatic transfer from grid tie to generator
> input.
> Brad Bassett
>
> On Thu, Oct 24, 2024 at 3:42 PM Wayne Irwin via RE-wrenches <
> [email protected]> wrote:
>
>> It is my understanding that the FXR will not "automatically" switch from
>> Grid Input to Gen.
>> To my knowledge this is a manual option only.
>> I do not recall any way to make this happen automatically. That would
>> have been great.
>> You can however still call for the generator at a low V setting and have
>> the generator power an external charger to boost the batteries.
>> I think the brand we used to use was IOTA however, I have also seen golf
>> cart chargers used.
>> Wayne Irwin
>> President
>> License #CVC56695
>> State Licensed Solar Contractor
>> Pure Energy Solar International Inc.
>> [email protected]
>> PureEnergySolar.com <http://pureenergysolar.com/>
>> SolarChargingStation.com <http://solarchargingstation.com/>
>> 352 377-6527 Office
>> 352 336-3299 Fax
>>
>>
>> The Sun Is Always Shining!
>>
>> The content of this message is Pure Energy Solar Confidential. If you are
>> not the intended recipient and have received this message in error, any use
>> or distribution is prohibited. Please notify me immediately by reply e-mail
>> and delete this message from your computer system. Thank you.
>> ------------------------------
>> *From:* RE-wrenches <[email protected]> on
>> behalf of Jay via RE-wrenches <[email protected]>
>> *Sent:* Thursday, October 24, 2024 5:57 PM
>> *To:* RE-wrenches <[email protected]>
>> *Cc:* Jay <[email protected]>
>> *Subject:* Re: [RE-wrenches] New Outback FXR Series as GTGBB on existing
>> Off Grid Home
>>
>> Hi Jeremy
>> There are two issues I think.
>> 1 is that the inverter won’t connect.
>> And I don’t have an answer why the inverter won’t in sell mode but will
>> in gen mode. Maybe the generator is slightly out of the more narrow window
>> for grid. I presume you’ve checked hz and volts and they are in spec for
>> grid?  I know sometimes the frequency control can be slightly variable
>> without a load. I’ve had success in the past getting inverters to connect
>> to a generator with putting some dumb loads on it. Like incandescent lights
>> or small heater.
>> 2. Maybe it’s a good thing it won’t because if it did connect wouldn’t it
>> be possible for the inverter to try to sell to the generator?  If you
>> didn’t have to change grid to Gen?
>> Jay
>>
>> On Oct 23, 2024, at 8:47 PM, Jeremy Rodriguez via RE-wrenches <
>> [email protected]> wrote:
>>
>> Wrenches,
>> We have a client that has brought utility power in and we now have the
>> system hooked up to the utility.
>> In setting the system up, I've experienced that the inverter will sell
>> and function fine with all the settings set up as* Grid Tied* mode, but
>> it does not play nice when the grid is gone , and the Generator is brought
>> in as the AC source.
>> We have installed an external transfer switch to switch the inverters' AC
>> input, from either the utility or the existing backup generator ( if the
>> grid fails), automatically.
>> The manual states that the inverter's two input selections can be
>> programmed for seperate input modes, via the* Input* *Type* menu. Ive
>> not been able to get this accomplished.
>> When simulating a grid outage, thus changing the AC input to the inverter
>> being from the Generator, the inverter will not synch to the AC power to
>> charge the batteries.
>> The only way that I can get the inverter to synch, is to switch the input
>> mode to *GEN* from *GRID.*
>> This is not ideal since the client would need to be present to make the
>> button push, even though the generator will be started automatically if the
>> grid were to go down (hopefully) , just as it did before.
>>
>> With no way to contact Outback , can someone advise how to properly
>> program the inverter/ MATE3S for this project?
>> Equipment onsite:
>> Single VFXR3648 inverter
>> Two FM60 CCs
>> Hub4
>> MATE3S
>> ATS with Dual Relays 50A
>> L.A. Battery bank
>> Here's how we would like it to work:
>> Utility power ON:
>> Sell excess power once the batteries have gone through the Absorb cycle.
>> Batteries remain full in case of a utility failure.
>> Utility Outage:
>> ATS now feeds Inv AC input via Generator if needed.
>> Inverter runs the home as it did , off grid.
>> If the battery voltage drops and the AGS is engaged, the inverter will
>> use that input to charge the batteries as usual.  If the grid comes back on
>> and the gen is running, the generator can still run, with no connection to
>> the inverter.  With the grid now charging the battery bank, and the AGS
>> will enventually shut off the Gen. Based on voltage.
>> Contact me off list if necessary
>> Jeremy Rodriguez
>> All Solar Inc.
>> Penrose, CO
>> 719-276-4954
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
>
> Sent from Finest Planet WebMail.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to