Hello Wrenches, I visited a site with a Sol-Ark 5k, 2P yesterday. They had complained of power shutdowns. There were a lot of F34 AC Overload faults.
I tracked it down to a single circuit. This circuit had a bank of about 12 LEDs, all on a single switch. The meter I brought, couldn't capture a significant inrush. The circuit had about 1A @120 Vac when running. It surprised me that these LEDs would cause this error, and perhaps there was something wrong with the LED driver (integrated in each bulb). I did a bit of research, and it looks like some LED drives can have extremely high inrush currents. It appears that these 12 drivers in parallel was enough to trip off the Sol-Ark. Curious if anyone else has ran into this. I did some research and it looks like there is a product called an inrush current limiter that we may be able to try. I pulled 4 of the bulbs and ran the whole house and switched it on and off and it worked fine about 10 x's. Is it possible that the Sol-Ark is overly protective of itself? The time scale on this inrush is typically 1-2 ms. Thanks for your input! -- Mac Lewis *"Yo solo sé que no sé nada." -Sócrates*
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org