An update on this “issue”. Sol-Ark Tech Support said that the high voltage DC 
is normal and not a concern. I believe they said it was a “static” voltage. 
They didn’t really provide an answer as to why it’s present. But I stick to my 
hypothesis that the source is the H-Bridge drive circuitry. 

William, to your point, I’m not thrilled that there’s a DC voltage on the AC 
output. But given that these units have been in operation for years without 
issue related to this input/output I’m not too worried.

Thanks everyone!

> On Oct 16, 2024, at 11:09 PM, William Miller <[email protected]> wrote:
> 
> Rick:
> 
> You’re OK leaving this random high voltage DC on the AC output?
> 
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com <http://www.millersolar.com/>
> 
> 
> On Wed, Oct 16, 2024 at 6:09 PM [email protected] 
> <mailto:[email protected]> <[email protected] 
> <mailto:[email protected]>> wrote:
>> Confirmed! Reading the same points on a different inverter yielded the same 
>> results. At a different site, I measured -188.8VDC to ground on both L1 and 
>> L2. 
>> 
>> My suspicion is that there’s leakage current via the H-bridge output. Just a 
>> thought. 
>> 
>> Case closed, thanks. 
>> 
>> Rick Brown
>> Solshine Energy 
>> Solar Electric Contracting Services 
>> www.solshineenergy.com <http://www.solshineenergy.com/>
>> Roanoke, VA
>> Office: 540.235.3095
>> Mobile: 540.808.9502
>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>> named in
>> 
>> the message header. Unless otherwise indicated, it contains information that 
>> is
>> 
>> confidential, privileged and/or exempt from disclosure under applicable law. 
>> If you have
>> 
>> received this message in error, please notify the sender of the error and 
>> delete the
>> 
>> message. Thank you.
>> 
>> 
>> 
>>> On Oct 16, 2024, at 3:49 PM, [email protected] 
>>> <mailto:[email protected]> wrote:
>>> 
>>> Sorry I wasn’t clear. There’s no PV tied directly to the Sol-Ark however 
>>> the Sunny Boy has 5.52 kW of PV. Again the SB is AC coupled to the Sol-Ark 
>>> via its Load input/output.
>>> 
>>> I can assure you that the DC is not coming from an external source. There 
>>> are no faults at either inverter (measured or indicated by the 
>>> inverter(s)). Both systems are operating normally.
>>> 
>>> I’ll be looking at another site to verify whether these readings are 
>>> consistent or an anomaly.
>>> 
>>> Thanks,
>>> Rick
>>> 
>>>> On Oct 15, 2024, at 3:49 PM, William Miller via RE-wrenches 
>>>> <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>> 
>>>> Rick:
>>>>  
>>>> Two questions:
>>>>  
>>>> 1.   If you don’t have PV on this system, what are those glassy, flat 
>>>> things on the roof wired to the DC inputs of your Sunny Boy?
>>>>  
>>>> 2.   Think to yourself: What component(s) on this project could possibly 
>>>> produce high voltage DC?
>>>>  
>>>> I think the answer to both questions is… PV panels.  I highly suspect you 
>>>> have a PV ground fault.  Proceed with caution.
>>>>  
>>>> On the Sunny Boy I would check the DC voltage between L1 and ground, 
>>>> between L2 and ground and between neutral and ground.  Do this in the 
>>>> operational configuration that is producing the DC voltage on the Gen 
>>>> inputs.
>>>>  
>>>> While you are at it, check DC voltages between the Sunny Boy DC inputs to 
>>>> ground and between the Sunny Boy Chassis and ground.
>>>>  
>>>> Check your GEC, GEC bonding conductor and all of the system EGCs.
>>>>  
>>>> I would also check the GFDI fuse on the Sunny Boy.  
>>>>  
>>>> William Miller
>>>>  
>>>> Miller Solar
>>>> 17395 Oak Road, Atascadero, CA 93422
>>>> 805-438-5600
>>>> www.millersolar.com <http://www.millersolar.com/>
>>>> CA Lic. 773985
>>>>  
>>>>  
>>>> From: [email protected] <mailto:[email protected]> 
>>>> [mailto:[email protected] <mailto:[email protected]>] 
>>>> Sent: Tuesday, October 15, 2024 12:03 PM
>>>> To: [email protected] <mailto:[email protected]>; RE-wrenches
>>>> Subject: Re: [RE-wrenches] Sol-Ark Gen Input
>>>>  
>>>> William,
>>>>  
>>>> There’s no PV on this system. It’s AC coupled to an SMA SB5.0. 
>>>>  
>>>> As a test, we turned off the Grid input, Load output, and turned off the 
>>>> battery breaker. As expected, the high voltage DC eventually bled to 0V. 
>>>> Turning things on in this order: Battery, Grid, then Load resulted in the 
>>>> high voltage appearing once the Grid relay kicked on. Actually, the high 
>>>> voltage ramped up slowly once the Grid relay turned on.
>>>>  
>>>> We’ve been installing these for years and have never seen this. Then 
>>>> again, we’ve never measured that point.
>>>> 
>>>> 
>>>> On Oct 15, 2024, at 2:32 PM, William Miller via RE-wrenches 
>>>> <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>>  
>>>> Rick:
>>>>  
>>>> If I had to guess I’d say you have a PV wiring fault.  The PV positive may 
>>>> be shorted to ground.  
>>>> This would make the inverter chassis negative in relation to ground.  
>>>>  
>>>> The logic I use is to ask what is the likely source of DC at 195 volts?  
>>>> It is most likely the PV circuits, wouldn’t you say?
>>>>  
>>>> If the DC Fault is not eternal then it must be internal to the inverter.  
>>>> This could be a dangerous situation.  I would proceed with caution.
>>>>  
>>>> Try completely isolating the PV from the inverter as a start.
>>>>  
>>>> Good luck.
>>>>  
>>>> William Miller
>>>>  
>>>> Miller Solar
>>>> 17395 Oak Road, Atascadero, CA 93422
>>>> 805-438-5600
>>>> www.millersolar.com <http://www.millersolar.com/>
>>>> CA Lic. 773985
>>>>  
>>>>  
>>>> From: RE-wrenches [mailto:[email protected] 
>>>> <mailto:[email protected]>] On Behalf Of rick--- 
>>>> via RE-wrenches
>>>> Sent: Tuesday, October 15, 2024 11:09 AM
>>>> To: RE-wrenches
>>>> Cc: [email protected] <mailto:[email protected]>
>>>> Subject: [RE-wrenches] Sol-Ark Gen Input
>>>>  
>>>> Back on the Sol-Ark topic again. We have a customer whose 12kW is 
>>>> measuring -195VDC to ground from L1 and L2 with the Gen breaker open. L1 
>>>> to L2 = 0V. I know the Gen input can be configured as an output, but 
>>>> reading a high DC voltage to ground is concerning. The generator has never 
>>>> been run. System is operating normally. 
>>>>  
>>>> Anyone have a Sol-Ark accessible that could verify what they’re reading?
>>>>  
>>>> Thanks in advance. 
>>>>  
>>>> Rick Brown
>>>> Solshine Energy 
>>>> Solar Electric Contracting Services 
>>>> www.solshineenergy.com <http://www.solshineenergy.com/>
>>>> Roanoke, VA
>>>> Office: 540.235.3095
>>>> Mobile: 540.808.9502
>>>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>>>> named in
>>>> 
>>>> the message header. Unless otherwise indicated, it contains information 
>>>> that is
>>>> 
>>>> confidential, privileged and/or exempt from disclosure under applicable 
>>>> law. If you have
>>>> 
>>>> received this message in error, please notify the sender of the error and 
>>>> delete the
>>>> 
>>>> message. Thank you.
>>>> 
>>>>  
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>  
>>>> rick brown
>>>> SolShine Energy Alternatives, LLC
>>>> Electrical & Solar Contracting Services
>>>> www.SolShineEnergy.com <http://www.solshineenergy.com/>
>>>> Roanoke, VA
>>>> Office: 540.235.3095
>>>> Mobile: 540.808.9502
>>>> 
>>>> VA Class A Contractor Lic# 2705147660
>>>> VA Master Electrician Lic# 2710062762
>>>> VA Alternative Energy Systems Installer  
>>>> NABCEP Certified PV Installation Professional 110112-21
>>>> 
>>>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>>>> named in
>>>> the message header. Unless otherwise indicated, it contains information 
>>>> that is
>>>> confidential, privileged and/or exempt from disclosure under applicable 
>>>> law. If you have
>>>> received this message in error, please notify the sender of the error and 
>>>> delete the
>>>> message. Thank you.”
>>>>  
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> rick brown
>>> SolShine Energy Alternatives, LLC
>>> Electrical & Solar Contracting Services
>>> www.SolShineEnergy.com <http://www.solshineenergy.com/>
>>> Roanoke, VA
>>> Office: 540.235.3095
>>> Mobile: 540.808.9502
>>> 
>>> VA Class A Contractor Lic# 2705147660
>>> VA Master Electrician Lic# 2710062762
>>> VA Alternative Energy Systems Installer  
>>> NABCEP Certified PV Installation Professional 110112-21
>>> 
>>> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) 
>>> named in
>>> the message header. Unless otherwise indicated, it contains information 
>>> that is
>>> confidential, privileged and/or exempt from disclosure under applicable 
>>> law. If you have
>>> received this message in error, please notify the sender of the error and 
>>> delete the
>>> message. Thank you.”
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergy.com
Roanoke, VA
Office: 540.235.3095
Mobile: 540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21

CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) named in
the message header. Unless otherwise indicated, it contains information that is
confidential, privileged and/or exempt from disclosure under applicable law. If 
you have
received this message in error, please notify the sender of the error and 
delete the
message. Thank you.”

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other: