Hi Nick

There are PF16's running open loop with Radians. The PF16 has a precharge
built in. The key is to have the inverter breaker closed, then close the
battery breaker. After that push the BMS power button (3-4 seconds the
display will power up) and the battery will slowly ramp up and do a
precharge before fully starting.

Reach out to me off the list and I can help you more if the "new" radian
does not work.

Thanks
Logan





On Sat, Nov 9, 2024 at 3:41 PM Nick Lucchese via RE-wrenches <
[email protected]> wrote:

> Greetings Wrenches,
>
> Wondering if any of you have successfully paired the new Powerflo16 with a
> GS8048-A yet? There is no reason it shouldn't work yet I've unsuccessfully
> been to a customer's site three times now without a fix. The Radian setup
> had been in use with an FLA Trojan pack for years till their demise due to
> the client unknowingly turned off the AC input source to keep them charged
> for his backup system lacking PV. Network is too far away therefore I
> didn't have Optics otherwise I would have caught it. Have not ruled out
> that there may have been another fault with the Radian before all this but
> the AC input seemed most logical and was known to be turned off by accident
> previously.
>
> Upon closing the Powerflo battery breaker to inverter the Mate3s lights up
> momentarily while briefly receiving full voltage but then DC voltage sinks
> to around 2-18vdc then either trips the breaker on the Powerflo16 or lights
> up the fault indicator. Spoke with Midnite support and they recommended a
> workaround to the BMS pre-charge boot up process but that didn't resolve
> the issue either. I originally thought it must be a failed Spare215 power
> supply board but after swapping there was no effect. Next return trip I
> brought a Rosie with me and everything powered up just fine so I then
> figured it would be the Spare 204 board stack but had the same exact effect
> when I tried that swap today. My next step is returning to swap the
> Spare-205 power control modules but first I'm going to unbox another
> Powerflo16 at my shop and pair it with a brand new Radian that has not yet
> been cannibalized. I've installed 42 Radians and only had two with failed
> Spare-205 control modules but each time it was a similar outcome with them
> being the last thing I swapped to success.
>
> I'm thinking it must be a failed Spare-205 but since the Powerflo has only
> been shipping for a couple months I just wanted to run this by the group to
> see how many have successfully paired these two components at this point.
> The Radian is still under warranty but that seems pretty meaningless at
> this point. One way or another this job is going to be a loss at this point
> but oddly still having fun working through a new head scratcher.
>
> Thanks for any insight, Nick
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to