Hi James, From my experience with older inverters it would have read zero.
When I got the answer from EG4 it makes sense. It also now makes sense that they are so nervous about what grounds are connected to the inverter buss as there is actually a connection to the power electronics. And that got me to thinking about other similar inverters. Sol ark Midnite gro watt thanks again jay > On Dec 10, 2024, at 4:46 PM, James Jarvis via RE-wrenches > <[email protected]> wrote: > > What voltage would you like it to read or what voltage are you expecting to > read? If I am understanding your post, you are measuring 120V Line to Neutral > and 120V Line to Ground. Ground has to "sit" somewhere and their explanation > of leakage current through the components is reasonable. > > If concerned about it further, then use your clamp on amp meter and measure > the current on the inverter output neutral and ground and make sure you don't > have any current flowing on ground. If the inverter is bonded internally and > there is another bond at the main panel and you are supply 120V loads, then > you would expect about half of the current to be on ground and half on > neutral. > > -James Jefferson Jarvis > APRS World, LLC > +1-507-454-2727 > http://www.aprsworld.com/ > > > On Tue, Dec 10, 2024 at 5:00 PM jay via RE-wrenches > <[email protected] > <mailto:[email protected]>> wrote: >> I just got an email back from them saying the following. >> >> >> There is no solid bond but the following will allow voltage to be detected >> between neutral and ground. >> Internal EMI filters or transient suppression devices that connect the AC >> lines to the ground. >> A small leakage path to ground via these components, which can result in >> measurable voltage. >> Is this common with other brands such as sol ark or midnite? >> >> thanks >> >> jay >> >> >>> On Dec 10, 2024, at 2:38 PM, jay <[email protected] >>> <mailto:[email protected]>> wrote: >>> >>> Hi All >>> >>> I just got off the phone with EG4 with the following situation and I wonder >>> if anyone has see this or can comment. >>> >>> With no wires attached, inverter ( LUX 6000XP) I read 120v from L1 to >>> ground and of course 120v to N. Yes it has an internal ground bond option >>> which is turned off. >>> >>> EG4 says this is normal go ahead and wire it up and that it’s fine that the >>> main panel some 15’ away is where that bonding is officially happening. >>> As I was worried that I was going to have 2 ground/neutral bonds. >>> >>> I’ve not seen this with our legacy inverters, could this be some kind of a >>> non solid connection?? >>> >>> I wonder if this is common with these types of inverters? >>> >>> thanks in advance. >>> >>> jay >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> <http://re-wrenches.org/> >> >> List Address: [email protected] >> <mailto:[email protected]> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/[email protected]/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >> > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org

