Hi Bruce,

I just had a similar situation, different batteries, and used the Iota DLS 48 / 
13 charger. Connected it directly to the cells bypassing the BMS, as it had 
opened the contactors to the regular power terminals. Took about 1hr of charge 
for the BMS to power up. I didn’t worry about any specific lithium settings or 
trying to close loop it, just used it as a jump start. We had other issues with 
the batteries that ended up being comms problems from being improperly 
configured preventing contactors from engaging. If it wasn’t for that, I expect 
would have been able to power up the inverter and resume normal charging within 
1hr.

Kevin

From: RE-wrenches <[email protected]> On Behalf Of 
Bruce Erickson via RE-wrenches
Sent: December-11-24 11:09 AM
To: RE-wrenches <[email protected]>
Cc: Bruce Erickson <[email protected]>
Subject: [RE-wrenches] SunPower SunVault black start

Recently one of our four now-orphaned SunVault systems failed to back up for 
our customer. On site we found the batteries discharged below cut-in voltage 
for unknown reasons (no more monitoring, no more tech support). Even though it 
had been sunny for a few days the system failed to retain a reserve to restart 
once sun returned. I’m looking for recommendations for 48 volt external 
chargers for this situation. We’re looking at Iota which only has a 13 amp 
charger at 48v but does have a plug-in module for controlling LiFePo charging. 
At 256 amphours of parallel batteries hopefully an 8 or 10 hour charge would 
get us up to cut-in. I’m also not sure how the Iota will play with any BMS the 
SunPower batteries might have. Any recommendations for this situation would be 
much appreciated.

Thanks in advance,
Bruce

Bruce Erickson
Mendocino Solar Service
707-937-1701
PO Box 1252
Mendocino, CA 95460


[cid:[email protected]]
"Serving the Solar System"





_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to