[sad]   Lloyd Hoffstatter reacted to your message:
________________________________
From: RE-wrenches <[email protected]> on behalf of Jay 
via RE-wrenches <[email protected]>
Sent: Saturday, December 14, 2024 12:41:44 AM
To: RE-wrenches <[email protected]>
Cc: Jay <[email protected]>
Subject: Re: [RE-wrenches] More Issues with Parallel Sol-Ark 15K System

Oh that’s not encouraging.

Care to share the issues.
At least the 18kpv is easy to set up.

Jay

On Dec 13, 2024, at 3:20 PM, Michael Morningstar via RE-wrenches 
<[email protected]> wrote:


I wish I didn't know what you guys were talking about :) !!! Both SS and S-A. 
As I've been going through my learning curve with Midnite's AIO and PF16, both 
Logan and Rick (and Richard at NAZ) have been there immediately for me and have 
held my hand the whole time.

On Fri, Dec 13, 2024 at 1:43 PM Jay via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Hi Jason

I had a similar situation at signature solar/eg4.

Customer was having lots of random issues with 18kpv. That included multiple 
shut downs per day.
After a few weeks of going through the same questions and answers I was able to 
find a good level 2 tech who agreed to replace the inverter.
They were just locked into it’s a ground loop, or something. And it’s monitored 
online. They can look at it.
14 days later the inverter arrived.
That’s good except it just showed up. No email, saying it shipped, nada.


So yeah they just don’t have any concept of tech support. I mean they do answer 
the phones but if they don’t have answers what good is it?
I do think it’s an issue with any growing company, more product more issues. 
Outback has gone through this process a few times, sometimes good, sometimes 
horrible. And of course the owner of Outback is also the owner of signature/eg4.

Midnight is different, and I plan to use their stuff when I get a chance.

FYI. I’ve got a 3 stack fortress 12kw
That has been running perfectly for 8 months now.

I’d say this is the new way, sucks.

Jay

On Dec 13, 2024, at 2:15 PM, Jason Szumlanski via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:


Just a follow-up to this saga... After many many more hours of diagnostics with 
tech support, often repeated on subsequent calls, I finally had to get 
irritated enough to demand that they just swap out the inverter. On three 
different calls they made me take the inverter out of parallel mode and run it 
standalone to see if it works, and it did. But when put back in parallel, it 
would fault out again. Today they made me put the subject inverter as the 
master in parallel mode, and it worked. Then I switched it back to its original 
slave position and it faulted out again. They had the audacity to tell me that 
some inverters are just like that and I should use it as the master. Obviously 
that is a ridiculous resolution to the problem. I demanded that they fix their 
faulty product under warranty and they are now sending me a replacement board 
and screen. I have a pretty good degree of confidence that it will fix the 
problem, but it really should not have been this hard to get to this point.

The troubleshooting process is broken at Sol-Ark. There is no continuum of 
severity that gets issues properly escalated and resolved. Repeated diagnostic 
measures just frustrate people and do not solve the issue. You have to get 
upset, and even nasty to speak to a supervisor. Meanwhile, the tier 1 agents 
are playing a game of telephone, relaying what the higher-ups are telling them 
to say. Some of them are knowledgeable, but many are just parroting what 
someone else to whispering in their ear, even when they don't have the full 
picture. It's like throwing spaghetti at a wall to see what sticks.

I will report back when I get the replacement parts and try them out.

Jason Szumlanski
Florida Solar Design Group

On Sat, Nov 9, 2024, 10:15 AM Jason Szumlanski 
<[email protected]<mailto:[email protected]>> 
wrote:
I wrote in another thread about an off-grid quad Sol-Ark system that was 
shutting down due to parallel stop when one of the four inverters experienced a 
DC PV fault, and how that shutdown is far from ideal. The same system is down 
once again, this time due to an AC fault code.

The homeowner started getting repeated F18 and F34 AC overcurrent faults on one 
of the slave inverters. This, in turn, shut the entire system down due to 
parallel stop faults (F41). None of the other units had AC overcurrent faults, 
and the load is nowhere near requiring all four inverters for even the most 
demanding circumstances. It was designed this way for redundancy, which I am 
quickly finding out is not Sol-Ark's strong suit.

To diagnose the issue remotely, I had the owner turn off all four load 
breakers, all DC PV input, and the AC microinverter input on the GEN terminals. 
I had them restart everything (several times). Every time, the same inverter 
would have repeated AC overcurrent faults, and the others would have parallel 
system faults. Since there were no loads connected by virtue of the load 
breakers being open, I suspected this had to be an internal fault.

I went to the site, and Sol-Ark Tier 1 tech support had me shut off all 
inverters and take the suspect inverter out of parallel operation mode. As a 
standalone master it was able to power up and support the entire house load 
without issue. Then we reprogrammed it for parallel operation again and turned 
everything back on. We were unable to stay on the phone long enough to 
determine if this was successful, but ultimately, the fault returned. I was 
told to call and ask for Tier 2 next time if it happened again, which I intend 
to do on Monday. At this point, the issue can only be internal to the unit, and 
I intend to demand warranty replacement of suspect components or the whole unit.

I had to get the system running, so I wanted to take the bad inverter out of 
the parallel system. I was hoping that simply shutting it down would work. This 
is the third of 4 inverters in the Modbus chain. When turning it off completely 
(all AC and DC switches disconnected), the 4th inverter would fault, presumably 
because the Modbus signal was not being relayed, but inverters #1 and #2 worked 
fine. However, I wanted #4 to also continue working while taking #3 out of 
service. So then I turned on the battery disconnect for #3 but left it in the 
off mode by not pressing the on/off button, thinking that it would allow relay 
of the Modbus signal from #2 to #4. That allowed the system to work 
momentarily, but then everything faulted out due to parallel system stop. In 
other words, I was going to have to physically take #3 out of the Modbus daisy 
chain to make this work.

Of course, I didn't have a long enough Cat5 cable with me, nor a Cat5 splice 
connector. So I had to rig something, which I did successfully to jumper from 
#2 to #4. But when I turned everything back on, #4 still would not work. I 
eventually realized that you have to change the Modbus address from 04 to 03 in 
the settings. Apparently, the addresses need to be sequential for it to work. 
Once I did this, I was able to get the system up and running again as a 
triple-inverter parallel setup. No faults were observed. So the theory was 
proven that #3 has an issue internally.


Anyway, bottom line, I am disappointed at how one inverter fault takes down the 
whole paralleled system, and also how taking a faulted inverter out of the 
system requires physical and programming changes. Turning it off should be 
sufficient. This is a very poor way to implement a parallel system that should 
provide the peace of mind that redundancy implies. Now I have a customer who 
thought they were getting a system with failsafe redundancy that actually 
requires a service call every time one of the paralleled units decides it does 
not want to play nicely with others.

Jason Szumlanski
Florida Solar Design Group

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: 
http://re-wrenches.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__re-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=l4SMGKfdKJPCvzQbuqUo5bGrdRcCTU9YX39elpc5ttE&e=>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.re-2Dwrenches.org_options.cgi_re-2Dwrenches-2Dre-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=JURh-m2gMIZA9OBkmsNuJz58PA1wWxDC9zHXf9HQKY0&e=>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.mail-2Darchive.com_re-2Dwrenches-40lists.re-2Dwrenches.org_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=srjhaBDLS2YDoh95YIDPeCsrapbQxoIMZ119rQQBX0w&e=>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.re-2Dwrenches.org_pipermail_re-2Dwrenches-2Dre-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=2rr6ICNHzWaCCMbZD2Fnx6HtyicrypUjpv7vfSnnYLw&e=>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.re-2Dwrenches.org_etiquette.htm&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=3Y7iEbFjZ8zEygO-LFNEFGjYESJ9AjvGJtFdYxzzGL8&e=>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.members.re-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=ZOb57quwYc6xiIBwHBwMz9sZqFErBTDcmGzQ2T84FNo&e=>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: 
http://re-wrenches.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__re-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=l4SMGKfdKJPCvzQbuqUo5bGrdRcCTU9YX39elpc5ttE&e=>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.re-2Dwrenches.org_options.cgi_re-2Dwrenches-2Dre-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=JURh-m2gMIZA9OBkmsNuJz58PA1wWxDC9zHXf9HQKY0&e=>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.mail-2Darchive.com_re-2Dwrenches-40lists.re-2Dwrenches.org_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=srjhaBDLS2YDoh95YIDPeCsrapbQxoIMZ119rQQBX0w&e=>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.re-2Dwrenches.org_pipermail_re-2Dwrenches-2Dre-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=2rr6ICNHzWaCCMbZD2Fnx6HtyicrypUjpv7vfSnnYLw&e=>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.re-2Dwrenches.org_etiquette.htm&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=3Y7iEbFjZ8zEygO-LFNEFGjYESJ9AjvGJtFdYxzzGL8&e=>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.members.re-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=BHECLcl9w3ZP_ABEVmxK_SfBSpvrl-DE8zBlR1vejxXMVT4kEoR7o3ueUyCqz7C3&s=ZOb57quwYc6xiIBwHBwMz9sZqFErBTDcmGzQ2T84FNo&e=>



--

Michael Morningstar


Morningstar Electric Inc

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

CSLB 1116835

[email protected]<mailto:[email protected]>


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to