Hey Mac,

            I've tried to calibrate the voltage displayed on the Mate with the Fluke on the battery bus bars but it doesn't seem to take after the adjustment in "calibrate".  But The Flexmax 80 does calibrate perfectly to the actual battery voltage and its in the FM80 aux landing that I'm using for this go-around to shut down the inverter to save the batteries.

            'Manually' meaning.....?

Thanks,

Bill

Feather River Solar Electric
Bill Battagin, owner
4291 Nelson St. (Shipping)
5575 Genesee Rd. (USPS, UPS)
Taylorsville, CA  95983
530-284-7849, 258-1641(cell)
CA. C10 Lic # 874049
Solar Powered since 1982
Home of the Sunny Side Up

On 1/2/2025 5:53 PM, Mac Lewis via RE-wrenches wrote:
Hi Bill,

Are all your voltages calibrated?  Mate, Flexmax, FM80? Where are you reading the voltages?

Does it work OK manually?



On Thu, Jan 2, 2025 at 12:08 PM Jay via RE-wrenches <[email protected]> wrote:

    Simpliphy has a very high voltage LVD.
    And the older OB can’t be programmed to those voltages



    On Jan 2, 2025, at 10:04 AM, Tyrone Houck via RE-wrenches
    <[email protected]> wrote:

    
    Forgive my ignorance but why won't the vfx lbco work for lithium?



    On Thu, Jan 2, 2025, 8:19 AM Bill Battagin via RE-wrenches
    <[email protected]> wrote:

        I am trying to use the "low battery disconnect" in aux mode
        in a newly
        installed OB FM80 CC for Li battery low voltage protection. I
        can't use
        the 19 year old OB VFX inverters for obvious reasons. The
        plan is to run
        the 12 volt output from the aux output to a NC relay to open
        it at 50
        VDC of the bank of SimpliPhi 3.8M batteries.  50 VDC is
        SimpliPhi's
        recommendation for LVD. The "output" of the relay would be
        connected to
        the VFX's  ON-OFF landings of that little green terminal
        block in the AC
        side of the inverter and just act as a simple switch for the
        inverter to
        turn it off to save the batteries.

                     I'm using one of my newer FM80's as a test run
        and have
        programmed the voltages in  Low Battery Disconnect mode and
        then put it
        in auto mode.  However, as the CC goes below the voltage set
        point, the
        AUX output does not turn on (time set for 5 seconds), as
        evidence in the
        CC's home screen and by checking for 12V at the AUX terminal
        block.

                     Any ideas of what I'm missing here to make this
        work? I
        know the other solution, thousands of $$ for new inverters
        which would
        be great but these folks have already invested quite a chuck
        on array
        replacement and charge controllers.

        Thanks for any experience with this.

        Bill

        Feather River Solar Electric
        Bill Battagin, owner
        4291 Nelson St. (Shipping)
        5575 Genesee Rd
        
<https://www.google.com/maps/search/5575+Genesee+Rd?entry=gmail&source=g>.
        (USPS, UPS)
        Taylorsville, CA  95983
        530-284-7849, 258-1641(cell)
        CA. C10 Lic # 874049
        Solar Powered since 1982
        Home of the Sunny Side Up


-- This email has been checked for viruses by Avast antivirus
        software.
        www.avast.com <http://www.avast.com>
        _______________________________________________
        List sponsored by Redwood Alliance

        Pay optional member dues here: http://re-wrenches.org

        List Address: [email protected]

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        There are two list archives for searching. When one doesn't
        work, try the other:
        https://www.mail-archive.com/[email protected]/
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        http://www.re-wrenches.org/etiquette.htm

        Check out or update participant bios:
        http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org



--



Mac Lewis

*

"Yo solo sé que no sé nada." -Sócrates

*

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


--
This email has been checked for viruses by Avast antivirus software.
www.avast.com
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to